The maximum stress in a "W 12 x 35" Steel Wide Flange beam , 100 inches long, moment of inertia 285 in 4 , modulus of elasticity 29000000 psi , with uniform load 100 lb/in can be calculated as
σ max = y max q L 2 / (8 I)
= (6.25 in) (100 lb/in) (100 in) 2 / (8 (285 in 4 ))
= 2741 (lb/in 2 , psi)
The maximum deflection can be calculated as
δ max = 5 q L 4 / (E I 384)
= 5 (100 lb/in) (100 in) 4 / ((29000000 lb/in 2 ) (285 in 4 ) 384)
= 0.016 in
Maximum moment in a beam with center load supported at both ends:
M max = F L / 4 (3a)
Maximum stress in a beam with single center load supported at both ends:
σ max = y max F L / (4 I) (3b)
F = load (N, lb)
Maximum deflection can be expressed as
δ max = F L 3 / (48 E I) (3c)
Forces acting on the ends:
R 1 = R 2
= F / 2 (3d)
The maximum stress in a "W 12 x 35" Steel Wide Flange beam, 100 inches long, moment of inertia 285 in 4 , modulus of elasticity 29000000 psi , with a center load 10000 lb can be calculated like
= (6.25 in) (10000 lb) (100 in) / (4 (285 in 4 ))
= 5482 (lb/in 2 , psi)
δ max = F L 3 / E I 48
= (10000 lb) (100 in) 3 / ((29000000 lb/in 2 ) (285 in 4 ) 48)
= 0.025 in
Maximum moment in a beam with single eccentric load at point of load:
M max = F a b / L (4a)
σ max = y max F a b / (L I) (4b)
Maximum deflection at point of load can be expressed as
δ F = F a 2 b 2 / (3 E I L) (4c)
R 1 = F b / L (4d)
R 2 = F a / L (4e)
Maximum moment (between loads) in a beam with two eccentric loads:
M max = F a (5a)
Maximum stress in a beam with two eccentric loads supported at both ends:
σ max = y max F a / I (5b)
δ F = F a (3L 2 - 4 a 2 ) / (24 E I) (5c)
R 1 = R 2
= F (5d)
Maximum moment (between loads) in a beam with three point loads:
M max = F L / 2 (6a)
Maximum stress in a beam with three point loads supported at both ends:
σ max = y max F L / (2 I) (6b)
Maximum deflection at the center of the beam can be expressed as
δ F = F L 3 / (20.22 E I) (6c)
R 1 = R 2
= 1.5 F (6d)
Dimensions and static properties of aluminum I-beams - Imperial units.
Area Moment of Inertia, Moment of Inertia for an Area or Second Moment of Area for typical cross section profiles.
Convert between Area Moment of Inertia units.
Estimate structures natural vibration frequency.
Moments and reaction support forces with distributed or point loads.
Calculate the acting forces and moments when elevating drawbridges or beams.
Properties of HE-M profile steel beams.
Convert between Elastic Section Modulus units.
Stiffness is resistance to deflection.
Support reactions and bending moments.
Common types of trusses.
Uniformly and concentrated floor loads
Allowable uniform loads.
Stress and deformation of vertical beams due to own weight.