Water Supply Lines - Sizing
Due to intermittent use of the fixtures in a water supply system it can be difficult to predict and size the supply and service lines. The fixtures total theoretical demand should always be compensated with a statistic more expected demand.
With the Water Supply Fixture Units (WSFU) system defined by the Uniform Plumbing Code (UPC) there are tables available where the total demand calculated by adding each units "Water Supply Fixture Units" (WFSU) are compensated to an expected demand.
The tables below can be used to size building supply and branch lines and meter and service lines.
Supply pressure 30 - 45 psi
Water Supply Lines - Sizing - Supply pressure 30 - 45 psi
Meter and street service lines
(inches)
Building supply and branch lines
(inches)
Maximum Water Supply Fixture Units (WSFU)
Length of pipe (feet)
406080100150200
3/4 1/2 6 5 4 3 2 1
3/4 19 16 14 12 9 6
1 29 25 23 21 17 15
1 1 36 31 27 25 20 17
1 1/4 54 47 42 38 32 28
Supply pressure 45 - 60 psi
Water Supply Lines - Sizing - Supply pressure 45 - 60 psi
(inches)
(inches)
406080100150200
3/4 1/2 7 7 6 5 4 3
3/4 20 20 19 17 14 11
1 39 39 36 33 28 23
1 1 39 39 39 36 30 25
1 1/4 78 78 76 67 52 44
Supply pressure over 60 psi
Water Supply Lines - Sizing - Supply pressure  > 60 psi
(inches)
(inches)
406080100150200
3/4 1/2 7 7 7 6 5 4
3/4 20 20 20 20 17 13
1 39 39 39 39 35 30
1 1 39 39 39 39 38 32
1 1/4 78 78 78 78 74 62
  • 1 in = 25.4 mm
The tables can be used for pipe lines but for special equipment like manifolds etc. a table or formula converting the WSFU to water flow should be used for proper sizing.
Water Systems
ASTM F876 - PEX Tube - Dimensions
Dimensions of PEX tubes.
BS 7291 - Thermoplastics Pipes for Hot and Cold Water - Dimensions
Dimensions of thermoplastic pipes - PEX and PB according BS 7291.
Cold Water Dwellings - Storage Capacities
Required cold water dwelling storage capacity - commonly used fixtures and types of buildings.
Cold Water Storage per Occupant
Cold water storage for occupants in common types of buildings as factories, hospitals, houses and more
Plumbing Codes
Plumbing or sanitation codes are a set of rules and regulations imposed by cities, counties or states.
Required Water Supply to Public Buildings
Water consumption and supply to public buildings.
Water Distribution Pipes - Materials
Materials used in water distribution pipes.
Water Service Pipe Lines
Water service pipe lines extends from the potable water source to the interior of buildings.
Calculating expected demand for water supply service lines.
Water Supply - Cross-Contamination Control
It is fundamental to keep the potable water in the water supply systems uncontaminated.
Water Supply Fixture Units - WSFU vs. GPM and Liters/sec
Converting WSFU - Water Supply Fixture Units - to GPM.
Yard Fixtures - Water Consumption
Water consumption in garden fixtures.