The total theoretical demand for a water supply system can easily be calculated by adding known maximum demand for all fixtures in the system. Due to the nature of intermittent use this will unfortunate add up to unrealistic demands for the main supply service lines. A realistic demand for a supply system will always be far less than the total theoretical demand.
Expected demand in a water supply system can be estimated as
qet = qnl + 0.015 (Σqn - qnl) + 0.17 (Σqn - qnl)1/2 (1)
qet = expected total water flow (l/s)
qnl = demand of largest consumer (l/s)
Σqn = total theoretical water flow - all fixtures summarized (l/s)
Note that minimum expected total water flow can never be less than the demand from the largest fixture. This equation is valid for ordinary systems with consumption patterns like
- homes
- offices
- nursing homes
- etc.
Be aware when using the equation for systems serving large groups of people where the use is intermittent, like in
- hotels
- hospitals
- schools
- theaters
- wardrobes in factories
- etc
For these kind of applications, like a wardrobe, it is likely that all showers are used at the same time. Using the formula blindly would result in insufficient supply lines.
Example - Main Water Supply to a Nursing Home
If the theoretical demand from all fixtures in a nursing home adds up to 50 l/s and the larges fixture requires 0.4 l/s, the expected water supply demand can be estimated like
qet = (0.4 l/s) + 0.015 ((50 l/s) - (0.4 l/s)) + 0.17 ((50 l/s) - (0.4 l/s))1/2
= 2.3 l/s
Total Theoretical Water Flow and Expected Flow
Expected demand for a supply system at different total theoretical demand can based on the formula above be expressed as
Total Theoretical Demand Summarized (liter/s) | Expected Demand (liter/s) |
0.2 | 0.2 |
0.8 | 0.4 |
1.6 | 0.5 |
4.0 | 0.6 |
8.0 | 0.85 |
15 | 1.1 |
20 | 1.5 |
30 | 1.8 |
40 | 2.1 |
65 | 2.8 |
70 | 2.9 |
100 | 3.7 |
The maximum fixture load is 0.2 liter/s.
• Water Systems
Domestic Hot Water Service Systems - Design Procedures
Design procedures for domestic hot water service systems.
Fixture Water Consumption and Required Water Supply
Supply requirements for common fixtures.
Required Water Supply to Public Buildings
Water consumption and supply to public buildings.
Water Consumption and Activities
Typical human activities and average water consumption
Water Distribution Pipes - Materials
Materials used in water distribution pipes.
Water Service Pipe Lines
Water service pipe lines extends from the potable water source to the interior of buildings.
Water Supply - Cross-Contamination Control
It is fundamental to keep the potable water in the water supply systems uncontaminated.
Water Supply Fixture Units - WSFU vs. GPM and Liters/sec
Converting WSFU - Water Supply Fixture Units - to GPM.
Water Supply Lines - Sizing
Sizing water supply service and distribution lines based on Water Supply Fixture Units (WSFU).
Water Supply Systems - Impurity Limits
Typiclal limits for impurities in drinking water.