q = measured air flow (ft 3 /min)
Δx = difference in humidity ratio (lb h2o /lb dry_air )
The latent heat flow due to moisture in air can be expressed in SI-units (metric) as
Q l = h we ρ q Δx / 3600 (2)
Q l = latent heat flow (kW)
h we = latent heat of vaporization of water ( 2454 kJ/kg - in air at atmospheric pressure and 20 o C)
ρ = air density at standard conditions ( 1.202* kg/m 3 )
q = air flow (m 3 /hr)
Δx = difference in humidity ratio ( kg h2o /kg dry_air )
*Note that properties of air changes with temperature. Interpolate values if necessary.
A ventilation system transports 10000 m 3 /h of air through a building.
The state of the make-up (supply) air is 0 o C and 100% relative humidity. From the Mollier diagram the humidity ratio - x - can be estimated to 0.0037 ( kg h2o /kg dry_air ) .
The state of the room air is 20 o C and 40% relative humidity. From the Mollier diagram the humidity ratio can be estimated to 0.0057 ( kg h2o /kg dry_air ) .
The latent heat flow can be calculated as
Q l = (2465.56 kJ/kg) (1.202 kg/m 3 ) (10000 m 3 /h) (( 0.0057 (kg h2o /kg dry_air ) ) - ( 0.0037 ( kg h2o /kg dry_air ) )) / 3600
= 16.5 kW
Air heating buildings - heat supply vs. air flow and temperature.
Latent and sensible cooling loads to consider when designing HVAC systems.
The Great Sensible Heat Factor is the ratio sensible to total heat in a cooling coil.
Latent heat of vaporization for fluids like alcohol, ether, nitrogen, water and more.
Melting and boiling point temperatures, latent heat of evaporation, and melting heat of common substances like copper, gold, lead and more - SI units.
Latent heat with vaporized propane.
Calculating heat removed with air by measuring the wet bulb temperature.
Room Sensible Heat Factor - RSHF - is defined as the sensible heat load divided by the total heat load in a room
Saturated Steam Table with properties like boiling point, specific volume, density, specific enthalpy, specific heat and latent heat of vaporization.
Sensible heat is dry heat causing change in temperature but not in moisture content
The ratio Sensible Heat (or Cooling) Load to the Total Heat (or Cooling) Load.
Vapor and steam enthalpy, specific enthalpy of saturated liquid, saturated vapor and superheated vapor.