Room Sensible Heat Factor - RSHF
The Room Sensible Heat Factor - RSHF - expresses the ratio between sensible heat load and total heat load in a room. It can be expressed as:
RSHF = Qsr / Qtr                           (1)
RSHF = room sensible heat factor
Qsr = sensible heat load in room (kW, Btu/hr)
Qtr = total heat load in room (kW, Btu/hr)
(1) can be modified to:
RSHF = cp (tr - ti) / (hr - hi)                                 (2)
cp = specific heat air (kJ/kg.oC)
tr = room temperature (oC)
ti = inlet temperature (oC)
hr = room enthalpy (kJ/kg)
hi = inlet enthalpy (kJ/kg)
Example - Room Sensible Heat Factor - RSHF
The sensible heat generated within a room is 4 kW. The latent heat generated is 1.4 kW.
The Room Sensible Heat Factor can be calculated as:
RSHF = (4 kW) / ((4 kW) + (1.4 kW))
= 0.75
Air Psychrometrics
Cooling and Heating Equations
Cooling Load - Latent and Sensible Heat
Latent and sensible cooling loads to consider when designing HVAC systems.
Great Sensible Heat Factor - GSHF
The Great Sensible Heat Factor is the ratio sensible to total heat in a cooling coil.
Heat Index
Equivalent heat index vs. air temperature and relative humidity - in degrees Fahrenheit and Celsius.
Human Heat Gain
Heat gain from persons in air conditioned spaces - in btu/hr.
Indoor Relative Humidity vs. Outdoor Relative Humidity and Temperature
Recommended indoor relative humidity vs. outdoor relative humidity and temperature.
Latent Heat Flow
Metabolic Heat Gain from Persons
Human metabolic heat gain in air conditioned rooms.
Sensible Heat Flow
Sensible heat is dry heat causing change in temperature but not in moisture content
Sensible Heat Ratio - SHR
The ratio Sensible Heat (or Cooling) Load to the Total Heat (or Cooling) Load.