Humid Air - Heating
The process of sensible heating of air - heating without adding moisture - can be visualized in the Mollier diagram as:
Sensible heating of air changes the state of the air from A to B along the constant specific humidity - x - line. The supplied heat - dH - can be estimated as indicated in the diagram above.
The heating process can also be visualized in the psychrometric chart
Note! - when sensible heating of air - the specific moisture remains constant - the relative humidity is decreased.
Calculating Enthalpy
The enthalpy of moist air can be calculated as:
h = cpa t + x (cpw t + hwe) (1)
h = specific enthalpy of moist air (kJ/kg)
cpa = 1.01 - specific heat capacity of air at constant pressure (kJ/kg oC, kWs/kgK)
t = air temperature (oC)
x = humidity ratio (kg/kg)
cpw = 1.84 - specific heat capacity of water vapor at constant pressure (kJ/kg. oC, kWs/kg.K)
hwe = 2502 - evaporation heat of water at 0 oC (kJ/kg)
(1) can be modified to:
h = 1.01 (kJ/kg. oC) t + x (1.84 (kJ/kg. oC) t + 2502 (kJ/kg)) (1b)
The Enthalpy Difference
The enthalpy difference when heating air without adding moisture can be calculated as:
dhA-B = cpa tB + x (cpw tB + hwe ) - cpa tA + x (cpw tA + hwe )
= cpa (tB - tA ) + x cpw (tB - tA ) (2)
Example - Enthalpy Change when Heating Air
The specific humidity of air at 25 oC and relative moisture 50% is 0.0115 kg/kg - check the Mollier diagram . The change in enthalpy when heating the air to 35 oC can be calculated as:
dhA-B = (1.01 kJ/kg oC)(35 oC - 25 oC) + (0.0115 kg/kg) (1.84 kJ/kg oC) (35 oC - 25 oC)
= (10.1 kJ/kg) + (0.2 kJ/kg)
= 10.3 (kJ/kg)
Note! - the contribution from the water vapor is relatively small and can for practical purposes often be neglected. (2) can then be modified to:
dhA-B = cpa ( tB - tA ) (2b)
Increase in Temperature when Heating Air
If heat is added to humid air the increase in air temperature can be calculated by modifying (2b) to:
tB - tA = dhA-B / cpa (2c)
Example - Heating Air and Temperature Rise
If 10.1 kJ is added to 1 kg air the temperature rise can be calculated as:
tB - tA = (10.1 kJ/kg) / (1.01 kJ/kg oC)
= 10 (oC)
Heat Flow in a Heating Coil
The total heat flow rate through a heating coil can be calculated as:
q = m (hB - hA ) (3)
q = heat flow rate (kJ/s, kW)
m = mass flow rate of air (kg/s)
The total heat flow can also be expressed as:
qs = L ρ (hB - hA ) (3a)
L = air flow rate (m3/s)
ρ = density of air (kg/m3)
Note! The density of air varies with temperature. At 0 oC the density is 1.293 kg/m3. At 80 oC the density is 1.0 kg/m3.
It's common to express sensible heat flow rate as:
q = m cpa (tB - tA ) (3b)
or alternatively:
q = L ρ cpa (tB - tA ) (3c)
Heating Coil Effectiveness
For a limited heating coil surface the average surface temperature will always be higher than the outlet air temperature. The effectiveness of a heating coil can be expressed as:
μ = (tB - tA ) / (tHC - tA ) (4)
μ = heating coil effectiveness
tHC = mean surface temperature of the heating coil (oC)
1 m3/s of air at 15 oC and relative humidity 60% (A) is heated to 30 oC (B). The surface temperature of the heating coil is 80 oC. The density of air at 20 oC is 1.205 kg/m3.
From the Mollier diagram the enthalpy in (A) is 31 kJ/kg and in (B) 46 kJ/kg.
The heating coil effectiveness can be calculated as:
μ = (30 oC - 15 oC) / (80 oC - 15 oC)
= 0.23
The heat flow can be calculated as:
q = (1 m3/s) (1.205 kg/m3) ((46 kJ/kg) - (31 kJ/kg))
= 18 (kJ/s, kW)
As an alternative, as one of the most common methods:
q = (1 m3/s) (1.205 kg/m3) (1.01 kJ/kg. oC) (30 oC - 15 oC)
= 18.3 (kJ/s, kW)
Note! Due to the inaccuracy when working with diagrams there is a small difference between the total heat flow and the sum of the latent and sensible heat. In general - this inaccuracy is within acceptable limits.
• Air Psychrometrics
Air - Drying Force
The drying force of air depends on the air moisture holding capacity and the water surface to air evaporation capacity.
Basic air changing state processes - heating, cooling, mixing, humidifying and dehumidifying by adding steam or water - psychometric diagrams and the Mollier charts.
Using steam to humidify air.
Air Cooling of Storage Roooms
Heat removed from storage rooms with cooled air.
Air Heating Systems
Air heating buildings - heat supply vs. air flow and temperature.
Cooling and Heating Equations
Cooling Load - Latent and Sensible Heat
Latent and sensible cooling loads to consider when designing HVAC systems.
Dry Air Thermodynamic and Physical Properties – Density, Specific Heat, Viscosity
THe essential thermodynamic properties of dry air like specific heat, ratio of specific heats, dynamic viscosity, thermal conductivity, Prandtl number, density and kinematic viscosity at temperatures ranging 175 - 1900 K.
Great Sensible Heat Factor - GSHF
The Great Sensible Heat Factor is the ratio sensible to total heat in a cooling coil.
Heat Recovery
Ventilation and heat-recovery calculations, sensible and latent heat - online calculators - imperial units.
Heat Recovery Efficiency
Latent Heat Flow
Moist Air - Cooling and Dehumidifying
Cooling and dehumidifying processes of moist and humid air - sensible and latent cooling.
Moist Air - Enthalpy
Removing Heat with Air
Calculating heat removed with air by measuring the wet bulb temperature.
Specific Heat Capacity of Air: Isobaric and Isochoric Heat Capacities at Various Temperatures and Pressures
Online calculator with figures and tables showing specific heat (Cp and Cv) of dry air vs. temperature and pressure. SI and imperial units.
Steam Heating Air