Heat Recovery
A heat-recovery system captures building exhaust air and reuse some of the energy to precondition the make-up air before supplying it to the building.
Air-to-air heat-recovery systems for comfort applications can in general be categorized as
  • sensible heat (dry bulb only) systems
  • total heat (wet bulb - sensible heat plus latent heat) systems
Sensible Heat-Recovery Systems
A sensible heat-recovery systems will transfer sensible (dry-bulb) heat from the exhaust air to the supply air entering the building. Rotary wheel heat exchangers and cross flow heat exchangers are some of the common designs used in typical comfort-to-comfort sensible heat-recovery applications.
The amount of heat transferred can be expressed as
H = 1.08 q (t2- t1) η                           (1)
H = heat transferred (Btu/h)
q = quantity of airflow (cfm)
t1 = air temperature of the exhaust air before the heat recovery unit (oF)
t2 = air temperature of outside air after the heat recovery unit (oF)
η = heat-recover efficiency
Example - A Sensible Heat Recovery System
The outside air temperature is 90ºF and the exhaust air temperature is 75ºF. The system operates at 40,000 cfm at 73 percent efficiency.
The sensible heat-recovery can be expressed as
H = 1.08 (40000 cfm) ((90 oF) - (75 oF)) 0.73
= 473040 (Btu/h)
A Sensible Heat Recovery Calculator
The calculator below can be used to calculate the sensible heat recovery where the air flow, outside and inside temperature and recovery efficiency are known.
Total Enthalpy Heat Recovery System
For total enthalpy heat-recovery systems the heat recovered can be expressed as
H = 4.5 q (h2- h1) η                         (2)
4.5 = (0.075 lbm/ft3) (60 min/h)
h1 = air enthalpy of the exhaust air before the heat recovery unit (Btu/lb)
h2 = air enthalpy of outside air after the heat recovery unit (Btu/lb)
Example - Total Enthalpy Heat Recovery System
The outside air wet-bulb temperature is 70ºF ( enthalpy 34 Btu/lb) and the exhaust-air wet-bulb temperature is 60ºF ( enthalpy 26.4 Btu/lb). The system operates at 40,000 cfm at 73 percent efficiency.
The total heat-recovery can be expressed like
H = 4.5 (40000 cfm) ((34 Btu/lb) - (26.4 Btu/lb)) 0. 73
= 998640 (Btu/h)
A Total Heat Recovery Calculator
The calculator below can be used to calculate the total (latent and sensible) heat recovery where the air flow, enthalpy of outside and inside air and the recovery efficiency are known.
Ventilation Systems
Air Heating Systems
Air heating buildings - heat supply vs. air flow and temperature.
Heat Recovery Efficiency
Humid Air - Heating
Moist Air - Enthalpy
Power Plants - Performance Efficiencies
Power plants heat rates, thermal efficiencies, capacity factors, load factors, economic efficiencies, operational efficiencies and energy efficiencies.