Steam Pipes - Sizing
The pressure available for distribution of steam is the pressure difference between the initial pressure at the boiler, and the required final pressure at the end of the line - at the steam consumer.
The pressure difference available for the distribution system can be expressed as:
p = pj - pk                                    (1)
p = available pressure drop (Pa (N/m2), psi (lb/ft2))
pj = initial or boiler pressure (Pa (N/m2), psi (lb/ft2))
pk = final pressure (Pa (N/m2), psi (lb/ft2))
The total pressure drop in the distribution system is a result of friction (major loss) and pressure loss in fittings (minor loss), and can be expressed as:
pt = pmajor + pminor                               (2)
pt = total pressure drop in the system (Pa (N/m2), psi (lb/ft2))
pmajor = pressure loss in pipes due to friction (Pa (N/m2), psi (lb/ft2))
pminor = pressure loss in fittings (Pa (N/m2), psi (lb/ft2))
Friction - Major Loss
Major loss - the pressure loss due to friction in a low pressure steam distribution system can be expressed as:
pmajor = pa l                                (3)
pa = pipe friction resistance per unit length of pipe (Pa/m (N/m2/m), psi/ft (lb/ft2/ft))
l = length of pipe (ft, m)
The pressure drop in a steam pipe can be expressed as
pa-100 = 0.01306 q2 (1 + 3.6/di) / (3600ρ di5)                                      (3b)
pa-100 = pressure drop per 100 ft pipe (psig / 100 ft)
q = steam flow rate (lb/h)
di = inside diameter of pipe (in)
ρ = density of steam (lb/ft3)
Loss due to Fittings - Minor loss
Loss due to fittings - minor loss can be expressed as:
pminor = ξ 1/2ρ v2                                 (4)
ξ = minor loss coefficient
pminor = pressure loss (Pa (N/m2), psi (lb/ft2))
ρ = density (kg/m3, slugs/ft3)
v = flow velocity (m/s, ft/s)
Equivalent length
Minor loss - loss due to fittings can also be expressed as equivalent length:
pminor = pa le                                (5)
or
pt = pa(l + le)                                 (6)
le = equivalent length of the fittings (ft, m)
As a rule of thumb the total pressure drop is about 5 -10% of initial pressure per 100 m pipe.
Typical Steam Velocities
  • Exhaust steam - 20 to 30 m/s (70 - 100 ft/s)
  • Saturated steam - 30 to 40 m/s (100 - 130 ft/s)
  • Superheated steam - 40 to 60 m/s (130 -200 ft/s)
Pipe Sizing
Sizing of steam and condensate pipe lines - pressure loss, recommended velocity, capacity and more.
Steam and Condensate
ANSI Schedule 40 Steel Pipes - Dimensions
Condensate Pipe Lines - Sizing
Flow and pressure loss in condensate return lines - SI Units.
Horizontal Pipe Hanger Supports - Spacing and Rod Size
Recommended maximum support span between hangers - and rod sizes for straight horizontal pipes.
Insulated Steam Pipes - Condensate Generated (kg/h per 100m)
Heat loss from steam pipes generates condensate which must be drained from the system.
Recommended Velocities in Steam Systems
The steam velocity in a steam distribution system should be within certain limits to avoid excessive wear and tear
Sizing Steam Pipes (kg/h)
Steam is a compressible gas where pipe line mass flow capacity depends on steam pressure.
Sizing Steam Pipes (lb/h)
Steam Flow Rate vs. Pressure Drop - Schedule 40 Pipe
Flow rate (lb/h) and pressure drop per 100 feet of pipe.
Steam Pipes - Installation of Drip Legs
Properly draining steam pipes for condensate.
Steam Pipes - Online Pressure drop Calculator
Calculate pressure drops in steam distribution pipe lines.
Steam Pipes - Pressure Drop vs. Steam Flow
Steam pipes and pressure drop diagrams - imperial and metric units.
Steam Trap Selection Guide
Steam trap selection guide - Float & Thermostatic, Inverted Bucket, Bimetal Thermostatic, Impulse and Thermodynamic Disc steam traps.
Steel Pipes - Thermal Expansion Loops
Calculating and sizing steel pipe thermal expansion loops.
Thermal Expansion of Steam Pipes - (inches)
Expansion of steam pipes heated from room temperature to operation temperature.