The total energy per mass unit in a given point in a fluid flow consists of elevation (potential) energy, velocity (kinetic) energy and pressure energy.
The Energy Equation states that energy can not disappear - the energy upstream in the fluid flow will always be equal to the energy downstream in the flow and the energy loss between the two points.
E1 = E2 + Eloss                                       (1)
E1 = energy upstream (J/kg, Btu/lb)
E2= energy downstream (J/kg, Btu/lb)
Eloss = energy loss (J/kg, Btu/lb)
The energy in a specific point in the flow
Eflow = Epressure + Ekinetic + Epotential                                   (2)
Epressure = p / ρ = pressure energy (J/kg, Btu/lb)
Ekinetic = v2 / 2 = velocity (kinetic) energy (J/kg, Btu/lb)
Epotential = g h = elevation (potential) energy (J/kg, Btu/lb)
Eloss = Δploss / ρ = major and minor energy loss in the fluid flow (J/kg, Btu/lb)
p = pressure in fluid (Pa (N/m2), psi (lb/in2))
Δploss = major and minor pressure loss in the fluid flow (Pa (N/m2), psi (lb/in2))
ρ = density of fluid (kg/m3, slugs/ft3)
v = flow velocity (m/s, ft/s)
g = acceleration of gravity (m/s2, ft/s2)
h = elevation (m, ft)
Eq. 1 and 2 can be combined to express the equal energies in two different points in a stream line as
p1 / ρ + v12 / 2 + g h1 = p2 / ρ + v22 / 2 + g h2 + Δploss / ρ                             (3)
or alternatively
p1 + ρ v12/ 2 + ρ g h1 = p2 + ρ v2 2/ 2 + ρ g h2 + Δploss                                (3b)
For a horizontal steady state flow v1 = v2 and h1 = h2, - and (3b) can be simplified to:
Δploss = p1 - p2                            (3c)
The pressure loss is divided in
  • major loss due to friction and
  • minor loss due to change of velocity in bends, valves and similar
The major friction loss in a pipe or tube depends on the flow velocity, pipe or duct length, pipe or duct diameter, and a friction factor based on the roughness of the pipe or duct, and whether the flow us turbulent or laminar - the Reynolds Number of the flow. The pressure loss in a tube or duct due to friction, major loss, can be expressed as:
Δpmajor_loss = λ (l / dh ) (ρ v2/ 2)                                 (4)
Δpmajor_loss = major friction pressure loss (Pa, (N/m2), lb/ft2)
λ = friction coefficient
l = length of duct or pipe (m, ft)
dh = hydraulic diameter (m, ft)
Eq. (3) is also called the D'Arcy-Weisbach Equation . (3) is valid for fully developed, steady, incompressible flow.
The minor or dynamic loss depends flow velocity, density and a coefficient for the actual component.
Δpminor_loss = ξ ρ v2 / 2                            (5)
Δpminor_loss = minor pressure loss (Pa (N/m2), lb/ft2)
ξ = minor loss coefficient
Head and Head Loss
The Energy equation can be expressed in terms of head and head loss by dividing each term by the specific weight of the fluid. The total head in a fluid flow in a tube or a duct can be expressed as the sum of elevation head, velocity head and pressure head.
Note ! The heads in the equations below are based on the fluid itself as a reference fluid. Read more about head here.
p1 / γ + v12 / 2 g + h1 = p2 / γ + v22 / 2 g + h2 + Δhloss                              (6)
Δhloss = head loss (m "fluid", ft "fluid")
γ = ρ g = specific weight of fluid (N/m3, lb/ft3)
For horizontal steady state flow v1 = v2 and p 1 = p2, - (4) can be transformed to:
hloss = h1 - h2                             (6a)
Δh = p / γ = head (m "fluid", ft "fluid")
The major friction head loss in a tube or duct due to friction can be expressed as:
Δhmajor_loss = λ (l / dh ) (v2 / 2 g)                          (7)
Δhloss = head loss (m, ft)
The minor or dynamic head loss depends flow velocity, density and a coefficient for the actual component.
Δpminor_loss = ξ v2 / (2 g)                            (8)
Friction Coefficient - λ
The friction coefficient depends on the flow - if it is
  • laminar,
  • transitional or
  • turbulent
and the roughness of the tube or duct.
To determine the friction coefficient we first have to determine if the flow is laminar, transitional or turbulent - then use the proper formula or diagram.
Friction Coefficient for Laminar Flow
For fully developed laminar flow the roughness of the duct or pipe can be neglected. The friction coefficient depends only the Reynolds Number - Re - and can be expressed as:
λ= 64 / Re                          (9)
Re = dimensionless Reynolds number
The flow is
  • laminar when Re < 2300
  • transitional when 2300 < Re < 4000
  • turbulent when Re > 4000
Friction Coefficient for Transitional Flow
If the flow is transitional - 2300 < Re < 4000 - the flow varies between laminar and turbulent flow and the friction coefficient is not possible to determine.
Friction Coefficient for Turbulent Flow
For turbulent flow the friction coefficient depends on the Reynolds Number and the roughness of the duct or pipe wall. On functional form this can be expressed as:
λ = f(Re, k / dh)                          (10)
k = absolute roughness of tube or duct wall (mm, ft)
k / dh = the relative roughness - or roughness ratio
Roughness for materials are determined by experiments. Absolute roughness for some common materials are indicated in the table below
Pressure Loss due to Friction - Roughness Coefficients vs. Surface Materials
SurfaceAbsolute Roughness - k
(10-3 m) (feet)
Copper, Lead, Brass, Aluminum (new) 0.001 - 0.002 3.3 - 6.7×10-6
PVC and Plastic Pipes 0.0015 - 0.007 0.5 - 2.33×10-5
Epoxy, Vinyl Ester and Isophthalic pipe 0.005 1.7×10-5
Stainless steel, bead blasted 0.001 - 0.006 (0.00328 - 0.0197) 10-3
Stainless steel, turned 0.0004 - 0.006 (0.00131 - 0.0197) 10-3
Stainless steel, electropolished 0.0001 - 0.0008 (0.000328 - 0.00262) 10-3
Steel commercial pipe 0.045 - 0.09 1.5 - 3×10-4
Stretched steel 0.015 5×10-5
Weld steel 0.045 1.5×10-4
Galvanized steel 0.15 5×10-4
Rusted steel (corrosion) 0.15 - 4 5 - 133×10-4
New cast iron 0.25 - 0.8 8 - 27×10-4
Worn cast iron 0.8 - 1.5 2.7 - 5×10-3
Rusty cast iron 1.5 - 2.5 5 - 8.3×10-3
Sheet or asphalted cast iron 0.01 - 0.015 3.33 - 5×10-5
Smoothed cement 0.3 1×10-3
Ordinary concrete 0.3 - 1 1 - 3.33×10-3
Coarse concrete 0.3 - 5 1 - 16.7×10-3
Well planed wood 0.18 - 0.9 6 - 30×10-4
Ordinary wood 5 16.7×10-3
The friction coefficient - λ - can be calculated by the Colebrooke Equation :
1 / λ1/2 = -2,0 log10( (2.51 / (Re λ1/2)) + (k / dh ) / 3.72)                             (11)
Since the friction coefficient - λ - is on both sides of the equation, it must be solved by iteration. If we know the Reynolds number and the roughness - the friction coefficient - λ - in the particular flow can be calculated.
A graphical representation of the Colebrooke Equation is the Moody Diagram :
With the Moody diagram we can find the friction coefficient if we know the Reynolds Number - Re - and the
Relative Roughness Ratio - k / dh
In the diagram we can see how the friction coefficient depends on the Reynolds number for laminar flow - how the friction coefficient is undefined for transitional flow - and how the friction coefficient depends on the roughness ratio for turbulent flow.
For hydraulic smooth pipes - the roughness ratio limits zero - and the friction coefficient depends more or less on the Reynolds number only.
For a fully developed turbulent flow the friction coefficient depends on the roughness ratio only.
Example - Pressure Loss in Air Ducts
Air at 0 oC is flows in a 10 m galvanized duct - 315 mm diameter - with velocity 15 m/s .
Reynolds number can be calculated:
Re = dh v ρ / μ                            (12)
Re = Reynolds number
v = velocity  (m/s)
ρ = density of air (kg/m3)
μ = dynamic or absolute viscosity (Ns/m2)
Reynolds number calculated:
Re = (15 m/s) (315 mm) (10-3 m/mm) (1.23 kg/m3) / (1.79×10-5Ns/m2)
= 324679 (kgm/s2)/N
= 324679 ~ Turbulent flow
Turbulent flow indicates that Colebrooks equation (9) must be used to determine the friction coefficient - λ -.
With roughness - ε - for galvanized steel 0.15 mm , the roughness ratio can be calculated:
Roughness Ratio = ε / dh
= (0.15 mm) / (315 mm)
= 4.76 10 -4
Using the graphical representation of the Colebrooks equation - the Moody Diagram - the friction coefficient - λ - can be determined to:
λ = 0.017
The major loss for the 10 m duct can be calculated with the Darcy-Weisbach Equation (3) or (6):
Δploss = λ ( l / dh ) ( ρ v2/ 2)
= 0.017 ((10 m) / (0.315 m)) ( (1.23 kg/m3) (15 m/s)2/ 2)
= 74 Pa N/m2
Fluid Mechanics
Ventilation Systems
A major friction loss diagram for air ducts - in imperial units ranging 10 000 - 400 000 cfm.
A major friction loss diagram for air ducts - SI units.
Air Ducts - Minor Loss Coefficient Diagrams
Minor loss coefficient diagrams for air ductwork, bends, expansions, inlets and outlets  - SI units.
Colebrook Equation
Copper Tubes - Pressure Loss vs. Water Flow
Water flow and pressure loss (psi/ft) due to friction in copper tubes ASTM B88 Types K, L and M.
Ducts - Sheet Metal Gauges
Thickness of sheet metal used in ductwork.
Energy and Hydraulic Grade Line
The hydraulic grade line and the energy line are graphical presentations of the Bernoulli equation.
Fluid Flow - Hydraulic Diameter
Calculate hydraulic diameter for pipes and ducts.
Hot Water Systems - Equivalent Length vs. Fittings Resistance
Equivalent length of fittings like bends, returns, tees and valves in hot water heating systems - equivalent length in feet and meter.
Laminar vs. Turbulent Flow - Reynolds Number Explained with Calculator
Lined Pipes - Pressure Loss vs. Water Flow
Pressure drop diagrams for PTFE, PP, PFA and PVDF lined pipes.
The Mechanical Energy Equation compared to the Extended Bernoulli Equation.
Moody Diagram
Calculate fluid flow friction coefficients from a Moody diagram.
Pipe and Tube System Components - Minor (Dynamic) Loss Coefficients
Minor loss coefficients for components used in pipe and tube systems.
Pressure Gradient Diagrams
Static pressure graphical presentation throughout a fluid flow system.
Steel Pipes - Maximum Water Flow Capacities vs. Size
Maximum water flow capacities in steel pipes - pipe dimensions ranging 2 - 24 inches.
Steel Pipes Schedule 40 - Pressure Loss
Water flow and pressure loss in schedule 40 steel pipes - Imperial and SI units - gallons per minute, liters per second and cubic meters per hour.
Surface Roughness Coefficients
Surface coefficients that can be used to calculate friction and major pressure loss for fluid flow with surfaces like concrete, galvanized steel, corroded steel and more.
System Curve and Pump Performance Curve
Utilize the system curve and the pump performance curve to select the proper pump for a particular application.
Velocity Classification of Ventilation Ducts
Recommended air velocities in ventilation ducts
Ventilation Ducts - Minor Loss Resistance
Minor pressure or head loss in ventilation ducts vs. air velocity - minor loss coefficient diagram.