Piping Elbows - Thrust Block Forces
In a piping structure without adequately support fluid flow and internal pressure may create intolerable forces and tensions.
The resultant force - or required support force - on a thrust block - or an anchor - for a bend depends on
- the fluid mass flow, or flow velocity
- the change of flow direction
- the internal pressure
With no flow and no pressure there is no force.
Online Pipe Bend Resulting Force Calculator
The calculator below can used to calculate the resulting force in a piping bend:
Metric Units
Imperial Units
Resulting force due to Mass flow and Flow Velocity
The resulting force in x-direction due to mass flow and flow velocity can be expressed as:
Rx = m v (1 - cos(β)) (1)
= ρ A v2 (1 - cos(β)) (1b)
= ρ π (d / 2)2 v2 (1 - cos(β)) (1c)
Rx = resulting force in x-direction (N)
m = mass flow (kg/s)
v = flow velocity (m/s)
β = turning bend angle (degrees)
ρ = fluid density (kg/m3)
d = internal pipe or bend diameter (m)
π = 3.14...
The resulting force in y-direction due to mass flow and flow velocity can be expressed as:
Ry = m v sin(β) (2)
= ρ A v2 sin(β) (2b)
= ρ π (d / 2)2 v2 sin(β) (2c)
Ry = resulting force in y direction (N)
The resulting force on the bend due to force in x- and y-direction can be expressed as:
R = (Rx2 + Ry2)1/2 (3)
R = resulting force on the bend (N)
Example - Resulting force on a bend due to mass flow and flow velocity
The resulting force on a 45o bend with
- internal diameter 102 mm = 0.102 m
- water with density 1000 kg/m3
- flow velocity 20 m/s
can be calculated by as
Resulting force in x-direction:
Rx = (1000 kg/m3) π ((0.102 m) / 2)2 (20 m/s)2 (1 - cos(45))
= 957 N
Resulting force in y-direction:
Ry = (1000 kg/m3) π ((0.102 m) / 2)2 (20 m/s)2 sin(45)
= 2311 N
Resulting force on the bend
R = (957 N)2 + (2311 N)2)1/2
= 2501 N
Note - if β is 90othe resulting forces in x- and y-directions are the same.
Resulting force due to Static Pressure
The pressure "acting" on the end surfaces of the bend creates resulting forces in x- and y-directions.
The resulting force in x-direction can be expressed as
Rpx = p A (1- cos(β)) (4)
= p π (d / 2)2 ( 1- cos(β)) (4b)
Rpx = resulting force due to pressure in x-direction (N)
p = gauge pressure inside pipe (Pa, N/m2)
The resulting force in y-direction can be expressed as
Rpy = p π (d / 2)2 sin(β) (5)
Rpy = resulting force due to pressure in y-direction (N)
Rp = (Rpx2 + Rpy2)1/2 (6)
Rp = resulting force on the bend due to static pressure (N)
Example - Resulting force on a bend due to pressure
- pressure 100 kPa
Rx = (100×103 Pa) π ((0.102 m) / 2)2 (1 - cos(45))
= 239 N
Ry = (100×103 Pa) π ((0.102 m) / 2)2 sin(45)
= 578 N
R = ((239 N)2 + (577 N)2)1/2
= 625 N
• Design Strategies for Piping Systems
Piping systems design strategies - documentation, P&ID, flow diagrams - capacities and limits.
• Pressure Ratings of Pipes and Fittings
Copper and Copper Alloy Pipes - Temperature Ranges
Bending copper pipe and tube temperatures.
Epoxy Pipes - Support Spacing
Support spacing for reinforced Epoxy fiberglass pipes.
Horizontal Pipe Hanger Supports - Spacing and Rod Size
Recommended maximum support span between hangers - and rod sizes for straight horizontal pipes.
Jet Propulsion
Calculate the propulsive discharge force or thrust induced by an incompressible jet flow.
Liquid Densities
Liquids - Specific Gravities
Specific gravities for common fluids like acetone, alcohol, turpentine, oil and more.
Nickel and Nickel Alloy Pipes - Temperature Ranges
Temperature ranges for bending nickel and nickel alloy pipes and tubes.
Pressfit Pipes - Supports
Maximum distance between pressfit pipe supports.
PVDF - PolyVinylidene Fluoride Pipes - Supports
Maximum distance between PVDF pipe supports.
Steel Pipes Expansion Loops - Design and Calculation
Steel pipe expansion loops and their importance in managing thermal expansion, and how to design and size them effectively. Key considerations, calculations, and installation tips to prevent stress and damage in piping systems.
Threaded Rods - Proof Loads - Metric Units
Proof load capacities of metric threaded steel rods.
Underground Pipes - Earth Pressure
Pressure acting on underground pipes due to weight of soil and transport.
Water Hammer
Rapidly closing or openingĀ valves - or starting stopping pumps - may cause pressure transients in pipelines known as surge or water hammer.