Underground Pipes - Earth Pressure
The pressure acting on an object in the ground - typical on the outside of a pipe can be calculated as
p = psoil + pwater + ptransport (1)
p = pressure acting on object in the ground (Pa)
psoil = pressure caused by the weight of the soil above the object (Pa)
pwater = hydrostatic pressure caused by the weight of the water above the object (Pa)
ptransport = pressure caused by the transport load on surface of the soil (Pa)
- 1 Pa = 10-6 N/mm2 = 10-3 kPa = 1.450x10-4 psi (lbf/in2)
Pressure caused by soil
psoil = ρs g (h - hw) + ρsw g hw (2)
ρs = density of soil above the groundwater (typical 1800 - 1900 kg/m3)
h = depth from surface to object (m)
hw = depth from groundwater level to object (m)
ρsw = density of soil below groundwater level (reduced due to Buoyancy of soil - typical value 1100 kg/m3)
Pressure caused by groundwater
pwater = ρw g hw (3)
ρsw = density water (1000 kg/m3)
Pressure caused by transport
The pressure caused by transport depends on the force (weight) on each wheel. The figure below indicates the the pressure at different depths for wheel force 75 kN (7500 kg) with dynamic factor 1.75.
Example - Pressure acting on an Underground Pipe
The pressure acting on pipe at buried at depth 2 m and 2 m below groundwater level can be calculated as
= 28449 Pa
= 28.5 kPa
pwater = (1000 kg/m3) (9.81 m/s2) (1 m)
= 9810 Pa
= 9.8 kPa
ptransport = aprox. from the diagram - 20 kPa
Total pressure
p = (28.5 kPa) + (9.8 kPa) + (20 kPa)
= 58 kPa
- 1 kPa = 1 kN/m2
Underground Pressure Calculator
This calculator is based on the equations below and can used to estimate the underground pressure acting on objects relatively smaller than the depth they are buried - typically pipes with diameter less than 3-500 mm.
Pressure from transport is calculated for wheel force 75 kN (7500 kg) with dynamic factor 1.75.
Bending PE Pipes
Bending PE pipe calculator.
Dirt and Mud - Densities
Densities - pound per cubic foot and kilograms per cubic metre - of dirt and mud.
Dimensions of PVC pipes according EN 1401.
EN 1451 - Polypropylene (PP) Plastics Piping Systems for Soil and Waste Discharge - Dimensions
Plastic piping systems for soil and waste discharge (low and high temperature) within the building structure.
Hydrostatic Force acting on Submerged Surface
Calculate the thrust force acting on a submerged surface.
Natural Gas Pipes - Minimum Cover
Burial dept and minimum cover of underground natural gas pipes.
Piping Elbows - Thrust Block Forces
Thrust block forces on pipe bends anchors due to liquid velocities and internal pressures - online resulting force calculator.
Soil and Rock - Bulk Factors