Water Hammer
A Surge or "Water Hammer" in pipe or tube is a pressure spike caused by sudden variation of flow rate.
"Water Hammer" can be created if
  • valves opens or closes to fast
  • pumps suddenly stops or starts
  • parts of the pipeline bursts
and velocity energy is converted to pressure energy. Since the water flow is restricted inside a pipe, a shock wave will travel forth and back through the incompressible water in the pipeline deflecting everything in its path.
Since liquids have a very low compressibility the resulting pressure energy can be very high. If the intensity in the shock wave is high, physical damage to the system can occur.
The Water Hammer pressure spike in a pipeline caused by closing or opening a valve can be estimated as
Δp = 0.070 Δv l / Δt                                      (1)
Δp = increase in pressure - pressure spike (psi)
Δv = change in flow velocity (ft/s)
Δt = valve closing time (s)
l = upstream pipe length (ft)
  • 1 ft (foot) = 0.3048 m
  • 1 ft/s = 0.3048 m/s
  • 1 psi (lb/in2) = 6894.8 Pa (N/m2)
Example - Water Hammer generated when closing a Solenoid Valve
The pressure spike (water hammer) in a 100 ft water pipe where the water flow velocity is reduced from 6 ft/s (1.8 m/s) to 0 ft/s (0 m/s) when a solenoid valve closes in 0.1 s - can be estimated as
Δp = 0.070 ((6 ft/s) - (0 ft/s)) (100 ft) / (0.1 s)
    = 420 psi
    = 29 bar
With a closing time of 1 s (solenoid valve with damper) - the pressure spike (water hammer) can be estimated as
Δp = 0.070 ((6 ft/s) - (0 ft/s)) (100 ft) / (1 s)
    = 42 psi
    = 2.9 bar
Note! - it is important to
  • open and close valves slowly, and
  • use soft starters to start / stop pumps
to avoid a water hammer damaging the piping system.
Note - Water Hammer may make more damage in low pressure applications.
Water Hammer Calculator
Imperial Units
SI Units
Pressure Ratings of Pipes and Fittings
Water Systems
ABS Pipes - Pressure Ratings
Pressure ratings of ABS 1208, ABS 1210, ABS 1316 and ABS 2112.
ASTM A312 Stainless Steel Pipes - Bursting and Collapsing Pressures
Theoretic bursting and collapsing pressures for stainless steel pipes ASTM A312.
ASTM A53 B Carbon Steel Pipes - Allowable Pressure vs. Schedule and Size
Maximum working pressure of carbon steel pipe at temperature 400oF.
Barlow's Formula - Calculate Internal, Allowable and Bursting Pressure
Calculate pipes internal, allowable and bursting pressure.
Bulk Modulus and Fluid Elasticities
Introduction to - and definition of - Bulk Modulus Elasticity commonly used to characterize the compressibility of fluids.
Carbon Steel Pipes - Pressure and Temperature Ratings, Imperial Units
Pressure (psig) and temperature (deg F) ratings for A-53 B and A-106 B, A333, A334 and API 5L carbon steel pipes - temperatures ranging 100 degF - 700 degF.
CPVC Pipes - Operating and Collapsing Pressures vs. Schedule and Size
Maximum operating and bursting pressures of CPVC - Chlorinated Poly (Vinyl Chloride) - piping systems.
Mach Number
An introduction to the Mach Number.
Piping Elbows - Thrust Block Forces
Thrust block forces on pipe bends anchors due to liquid velocities and internal pressures - online resulting force calculator.
Positive Displacement Pumps
Introduction tutorial to positive displacement pumps basic operating principles.
Stainless Steel Pipes - Allowable Pressure vs. Schedule and Size
Allowable pressure for standard seamless A312-TP316/316L stainless steel pipes - temperatures 100oF to 750oF.
Wrought Steel Pipes - Bursting Pressures vs. Size
Theoretical bursting and working pressure of wrought steel standard, extra strong and double extra strong pipes.