Water Control Valves - Flow Factor Kv Diagram
The flow factor Kv for control valves in water systems can be estimated from the diagram below:
- 1 bar = 1x105 Pa (N/m2)
Example - a Water Valve and Kv value
The maximum pressure drop through a modulating control valve in a water flow system is designed to be 100 kPa. The flow through the valve is 5 liter/s. The required kv value for the valve can be estimated as indicated in the diagram below to approximately 20.
Note - larger valves (with larger Kv) reduces the maximum pressure modulating spans - limiting the ability to provide a stable process control. As a consequence - control valves are often one to two dimensions below the dimensions of the connecting pipes.
Example - with a water flow of 5 liter/s the pipe size would be in the range 3 - 4 inches (80 - 100 mm nominal). A control valve would be in the size kv ~ 20 - or in the range 2 - 3 inches (50 - 80 mm nominal).
• Control Valves
Control Valve terminology, bodies, trim, flow characteristics, Cv and Kv sizing, noise, actuators and positioners
Ball Valves - Flow Coefficients Cv
Flow coefficients - Cv - for typical ball valves - reduced and full bore.
Flow Coefficient Cv vs. Flow Factor Kv
Comparing flow coefficients Cv to flow factors Kv.
Liquid, Steam and Gas - Flow Factor Kv
Calculate flow factor Kv for liquids, steam and gases - metric units.
Straight Through Diaphragm Valves - Flow Coefficients
Flow coefficients - Cv - and flow factors - Kv - for straight through diaphragm valves.
Valve Authority
The valve authority expresses the ratio between pressure drop across the control valve compared to total pressure drop across the whole system.
Valves Types - Operating Size Ranges
Types of valves and their typical operating sizes.
Water Control Valves - Flow Coefficient Cv Diagram
Sizing of water control valves - Imperial units.
Water Control Valves - Kv Calculation
Designing water process control valves and their Kv values.