Pressure loss in hot water steel piping systems can be estimated from the nomogram below:
The heat flow is based on temperature difference 20 oC.
  • 1 Pa = 10-6 N/mm2 = 10-5 bar = 0.1020 kp/m2 = 1.02×10-4 m H2O = 9.869×10-6 atm = 1.45×10-4 psi (lbf/in2)
  • 1 kW = 1,000 Watts = 3,412 Btu/h = 737.6/550 British hp = 1.341 British hp = 103/9.80665 kgf m/s = 737.6 ft
  • 1 liter/s = 10-3 m3/s = 3.6 m3/h = 0.03532 ft3/s = 2.1189 ft3/min (cfm) = 13.200 Imp.gal (UK)/min = 15.852 gal (US)/min = 792 Imp. gal (UK)/h
  • m (meter) = 3.2808 ft = 39.37 in = 1.0936 yd = 6.214×10-4 mile
Example - Pressure Loss in a Hot Water Heating Pipe
The pressure loss in a 2" BS 1387 hot water heating pipe with heat flow 100 kW can be estimated as indicated below
  • With temperature difference 20 oC the water flow is 1.2 liter/s
  • The flow velocity is 0.54 m/s
  • The pressure loss is 60 Pa/m
Fluid Mechanics
Heating Systems
ANSI Steel Pipe Schedule 40 Chart: Dimensions, Weights & Specifications
ASME/ANSI B36.10/19 - Carbon, Alloy and Stainless Steel Pipe - Dimensions
Design of Hot Water Heating Systems
Calculate gravity and forced circulating hot water heating systems.
Gravity Heating System
The density difference between hot and cold water is the circulating force in a self circulating gravity heating system.
Heating System Flow Rates
Calculate flow rates in heating systems.
Heating Systems - Safety Valve Size vs. Boiler Power
Hot Water Expansion Tanks - Sizing
Required hot water expansion volume in open, closed and diaphragm tanks.
Hot Water Heating System - Design Procedure
Hot water heating system design procedure with heat loss, boiler rating, heater units and more.
Hot Water Heating System Online Design Application
Hot Water Heating System Temperatures vs. Outdoor Temperatures
Hot water heating temperatures adapts to outdoor temperatures.
Hot Water Heating Systems - Flow Temperatures vs. Outside Temperatures
Seasonal effects on hot-water heating systems flow temperatures.
Hot-Water Heating Systems - Classification
Hot-water heating systems can be classified by temperature and pressure.
ISO 4437 - PE Pipes for Gaseous Fuels Supply - Dimensions
Steel Pipes Schedule 40 - Friction Loss vs. Water Flow Diagram
Friction loss and velocity diagrams - in imperial (psi/100 ft, ft/s) and SI (Pa/100m, m/s) units.