Gravity Heating System
A self circulation heating system operates by the force created by the density difference between hot and cold fluid.
Gravity Head
The head forcing circulation through a gravity system is proportional to the elevation - he - of the heating elements (or radiators) above the boiler, and the temperature difference between the flow and return pipe lines.
The head available for circulation can be calculated
hl = hr (ρr - ρf) / ((ρr + ρf) / 2) (1)
hl = head available for circulation (m, ft)
hr = height of radiator or heating element above boiler (m, ft)
ρf = density of water in flow (hot) pipe (lb/ft3, kg/m3)
ρr = density of water in return (cold) pipe (lb/ft3, kg/m3)
The thermal expansion of water is approximately 4.2% from 4 oC to 100 oC.
Converting Head to Pressure
Head units can be converted to pressure units as
p = hl ρ g (2)
p = pressure (Pa, N/m2) - Other units?
ρ = density (kg/m3) (using hot or cold density has little impact in this calculation)
Circulating Pressure - Flow and Return Temperature
The forcing pressures in self circulation system with operating temperatures between 50 to 95 oC are indicated in the diagram and table below.
| Return Temperature (oC) | Circulating Pressure in Pa (N/m2) per m circulating elevation - he | |||||
| Flow Temperature (oC) | ||||||
| 40 | 50 | 60 | 70 | 80 | 90 | |
| 90 | 0 | |||||
| 80 | 0 | 64 | ||||
| 70 | 0 | 59 | 123 | |||
| 60 | 0 | 54 | 113 | 177 | ||
| 50 | 0 | 48 | 101 | 161 | 225 | |
| 40 | 0 | 41 | 89 | 143 | 203 | 267 |
• Heating Systems
Design of Hot Water Heating Systems
Calculate gravity and forced circulating hot water heating systems.
Hot Water Heating System Online Design Application
Pressure loss nomogram for hot water steel pipes.
Hot-Water Heating Systems - Classification
Hot-water heating systems can be classified by temperature and pressure.