Heating System Flow Rates
The volumetric flow rate in a heating system can be expressed as
q = h / (cp ρ dt)                          (1)
q = volumetric flow rate (m3/s)
h = heat flow rate  (kJ/s, kW)
cp = specific heat (kJ/kg oC)
ρ = density (kg/m3)
dt = temperature difference  (oC)
This generic equation can be modified for the actual units - SI or imperial - and the liquids in use.
Volumetric Water Flow Rate in Imperial Units
For water with temperature 60 oF flow rate can be expressed as
q = h (7.48 gal/ft3) / ((1 Btu/lbm oF) (62.34 lb/ft3) (60 min/h) dt)
= h / (500 dt)                           (2)
q = water flow rate (gal/min)
h = heat flow rate (Btu/h)
ρ = density (lb/ft3)
dt = temperature difference (oF)
For more exact volumetric flow rates the properties of hot water should be used.
Water Mass Flow Rate in Imperial Units
Water mass flow can be expressed as:
m = h / ((1.2 Btu/lbm. oF) dt)
=  h / (1.2 dt)                                      (3)
m = mass flow (lbm/h)
Volumetric Water Flow Rate in SI-Units
Volumetric water flow in a heating system can be expressed with SI-units as
q = h / ((4.2 kJ/kg oC) (1000 kg/m3) dt)
= h / (4200 dt)                                     (4)
q = water flow rate (m3/s)
h = heat flow rate (kW or kJ/s)
Water Mass Flow Rate in SI-units
Mass flow of water can be expressed as:
m = h / ((4.2 kJ/kg oC) dt)
= h / (4.2 dt)                                       (5)
m = mass flow rate (kg/s)
Example - Flow Rate in a Heating System
A water circulating heating systems delivers 230 kW with a temperature difference of 20 oC .
The volumetric flow can be calculated as:
q = (230 kW) / ((4.2 kJ/kg oC) (1000 kg/m3) (20 oC))
= 2.7 10 -3 m3/s
The mass flow can be expressed as:
m = (230 kW) / ((4.2 kJ/kg oC) (20 oC))
= 2.7 kg/s
Example - Heating Water with Electricity
10 liters of water is heated from 10 oC to 100 oC in 30 minutes . The heat flow rate can be calculated as
h = (4.2 kJ/kg oC) (1000 kg/m3) (10 liter) (1/1000 m3/liter) ((100 oC) - (10 oC)) / ((30 min) (60 s/min))
= 2.1 kJ/s (kW)
The 24V DC electric current required for the heating can be calculated as
I = (2.1 kW) (1000 W/kW) / (24 V)
= 87.5 Amps
Heating Systems
District Heating - Heat Capacity vs. Temperature
Water temperature and heating capacity.
Heating Systems - Safety Valve Size vs. Boiler Power
Heating Up Applications - Energy Required and Heat Transfer Rates
Energy required to heat up a substance.
Hot Water Boiler - Circulation Rates
Boiler power and water flow - Imperial and SI-units.
Hot Water Expansion Tanks - Sizing
Required hot water expansion volume in open, closed and diaphragm tanks.
Hot Water Heating System Online Design Application
Hot Water Heating System Temperatures vs. Outdoor Temperatures
Hot water heating temperatures adapts to outdoor temperatures.
Hot Water Heating Systems - Flow Temperatures vs. Outside Temperatures
Seasonal effects on hot-water heating systems flow temperatures.
Pressure loss nomogram for hot water steel pipes.