Heating Systems - Safety Valve Size vs. Boiler Power
Fired pressure vessels shall be fitted with safety relieving devices with sufficient capacity to relieve all vapor that may be generated in the vessels during normal operation. The safety relieving devices shall be fitted with proper controls to ensure safe operation.
Heating Systems - Safety Valves vs. Boiler Power
Boiler rating
(kW)
Minimum clear bore
of safety valves and vents
(mm)
275 1 x 20
350 1 x 25
440 1 x 32
530 1 x 40
880 2 x 40
1500 80 to 150
Note! Check domestic regulations - Safety Valve Standards
  • 1 kW = 3412 Btu/h
  • 1 inch = 25.4 mm
Safety valves should be removed at least once each year for inspection and cleaning of any deposits that might affect their operation.
To eliminate the necessity of shutting the system down for the inspection, a three-way stop valve may be installed under 2 safety valves, each with the required relieving capacity, installed so that both safety valves cannot be closed off from the vaporizer at the same time. Alternatively may 2 or more separate safety valves be installed with individual shutoff valves, in which case the shutoff valve stems is mechanically interconnected in a manner that allow full required flow capacity at all times.
Heating Systems
International Valve Standards
International valve standards for piping systems.
Pressure Ratings of Pipes and Fittings
Factors of Safety - FOS
Factors of Safety - FOS - are important in engineering designs.
Heating System Flow Rates
Calculate flow rates in heating systems.
High Pressure Steam Systems - Safety Valve Capacities
Sizing safety valves according boiler output power in high pressure systems (kW and Btu/hr)
Hot Water Heating System Online Design Application
Pressure loss nomogram for hot water steel pipes.
Hot-Water Heating Systems - Classification
Hot-water heating systems can be classified by temperature and pressure.
Low Pressure Steam Safety Valves - Capacities
Sizing safety valves after boiler output power in low pressure systems (kW and Btu/hr).
Pilot Operated Safety Valves in Liquid Systems
Calculate pilot operated relief valves in liquid systems.
Relief Valves - Length of Vent Pipes
Calculate length of safety valves vent pipes.
Safety Relief Valves - Capacity vs. Pressure
Maximum safety valve free air relief capacity.
The most common used safety valve standards in Germany, UK, USA, France, Japan, Australia and Europe.
Safety Valves in Gas and Vapor Systems
Calculating relief valves in gas and vapor systems.
Safety Valves in Saturated Steam Systems
Calculate safety valves in saturated steam systems
Spring Operated Safety Valves in Liquid Systems
Calculate spring operated relief valves in liquid systems.
Valve Type Classifications
Categories of valves.
Valves Types - Operating Size Ranges
Types of valves and their typical operating sizes.