Valve Authority
Control valve authority can be expressed as
N = dpv / (dpv + dpc) (1)
N = valve authority
dpv = pressure drop across a full open control valve (psi, Pa, kPa, bar)
dpc = pressure drop across the circuit (psi, Pa, kPa, bar)
To obtain control it is recommended that the control valve size is selected so that its authority is never less than 0.5. In general valve authority between
- 0 - 0.25 -> unstable to fair control
- 0.25 - 0.5 -> fair to good control
- 0.5 - 1.0 -> good control
Example - Control Valve Authority in a Heating System
The total pressure drop in a heating system circuit at full load is 15 kPa. The volume flow is 1.4 l/s.
For decent control the valve authority is set to N = 0.8. The pressure drop across the control valve dpv can be calculated by transforming (1) to
dpv = N dpc / (1 - N) (1b)
- or with values
dpv = 0.8 (15 kPa) / (1 - 0.8)
= 60 kPa
The flow factor for the valve with volume flow 1.4 l/s can be estimated to approximately
Kv = 7
by using this flow factor diagram. For a Straight Through Diaphragm Valve of "Saunders" type this corresponds to a 15 mm valve.
• Control Valve Sizing
API 6D Valves - Pressure Ratings vs. Temperature
Temperature and pressure ratings for valves according API 6D.
ASTM A216 Valves - Pressure Ratings vs. Temperature
Pressure and temperature ratings for cast carbon steel valves.
Ball Valves - Flow Coefficients Cv
Flow coefficients - Cv - for typical ball valves - reduced and full bore.
Control Valves - Cavitation
Control valves and cavitation, application ratio and multi stage control valves.
Control Valves - Flow Characteristics
Flow capacities vs. stem opening.
Control Valves for Water Flow – Kv Sizing & Pressure Drop Calculations
Control valve sizing and pressure drop calculations for water flow applications. Different valve types, Kv flow coefficients, and how to select the right valves.
Liquid, Steam and Gas - Flow Factor Kv
Calculate flow factor Kv for liquids, steam and gases - metric units.
Steam Control Valves - Calculate Flow Factor Kv
Designing steam control valves and their Kv values.
Straight Through Diaphragm Valves - Flow Coefficients
Flow coefficients - Cv - and flow factors - Kv - for straight through diaphragm valves.
Valve Selection Guide
Applications guide for selecting valves.
Valves - Specific Services
Valves - Typical Operating Temperatures
Operating temperatures for typical categories of valves - ball valves, butterfly valves and more.
Valves Types - Operating Size Ranges
Types of valves and their typical operating sizes.
Water Control Valves - Flow Factor Kv Diagram
Water Control Valves - Flow Coefficient Cv Diagram
Sizing of water control valves - Imperial units.