In a steam system with 9 bar gauge pressure the absolute pressure is 10 bar. If a pressure drop of 3.5 bar is acceptable and suitable for the steam consumer, the pressure coefficient Pcoef should be 18.4.
Select the pressure coefficient - Pcoef - column closest possible to the actual pressure coefficient calculated in step 1.
Follow the column down until reaching the appropriate actual flow value. Interpolate between values if necessary.
Go left in the table to find the actual flow factor Kv.
Kv | Steam Flow (kg/h) | |||||||||
Pressure Coefficient - Pcoeff | ||||||||||
1 | 1.25 | 1.56 | 1.95 | 2.44 | 3.05 | 3.81 | 4.77 | 5.96 | 7.45 | |
0.01 | 0 | 0 | 0 | 0 | 0 | 1 | 1 | 1 | 1 | 1 |
0.02 | 0 | 1 | 1 | 1 | 1 | 1 | 1 | 1 | 1 | 1 |
0.02 | 1 | 1 | 1 | 1 | 1 | 1 | 1 | 2 | 2 | 2 |
0.03 | 1 | 1 | 1 | 1 | 2 | 2 | 2 | 2 | 3 | 3 |
0.05 | 2 | 2 | 2 | 2 | 3 | 3 | 3 | 4 | 4 | 4 |
0.08 | 2 | 3 | 3 | 3 | 4 | 4 | 5 | 5 | 6 | 7 |
0.11 | 4 | 4 | 5 | 5 | 6 | 6 | 7 | 8 | 9 | 10 |
0.17 | 5 | 6 | 7 | 8 | 8 | 9 | 11 | 12 | 13 | 15 |
0.26 | 8 | 9 | 10 | 11 | 13 | 14 | 16 | 18 | 20 | 22 |
0.38 | 12 | 14 | 15 | 17 | 19 | 21 | 24 | 27 | 30 | 33 |
0.58 | 18 | 20 | 23 | 26 | 29 | 32 | 36 | 40 | 45 | 50 |
0.86 | 27 | 31 | 34 | 38 | 43 | 48 | 54 | 60 | 67 | 75 |
1.3 | 41 | 46 | 51 | 57 | 64 | 72 | 80 | 90 | 100 | 112 |
2.0 | 62 | 69 | 77 | 86 | 96 | 108 | 120 | 135 | 151 | 168 |
2.9 | 93 | 103 | 116 | 129 | 145 | 162 | 181 | 202 | 226 | 253 |
4.4 | 139 | 155 | 174 | 194 | 217 | 242 | 271 | 303 | 339 | 379 |
6.6 | 208 | 233 | 260 | 291 | 325 | 364 | 407 | 455 | 508 | 568 |
9.9 | 312 | 349 | 390 | 436 | 488 | 546 | 610 | 682 | 763 | 853 |
14.8 | 468 | 524 | 586 | 655 | 732 | 818 | 915 | 1023 | 1144 | 1279 |
22.2 | 703 | 786 | 878 | 982 | 1098 | 1228 | 1373 | 1535 | 1716 | 1918 |
33.3 | 1054 | 1179 | 1318 | 1473 | 1647 | 1841 | 2059 | 2302 | 2574 | 2877 |
49.9 | 1581 | 1768 | 1976 | 2210 | 2471 | 2762 | 3088 | 3453 | 3860 | 4316 |
74.8 | 2372 | 2652 | 2965 | 3315 | 3706 | 4143 | 4632 | 5179 | 5790 | 6474 |
112 | 3558 | 3978 | 4447 | 4972 | 5559 | 6215 | 6948 | 7769 | 8686 | 9711 |
168 | 5336 | 5966 | 6671 | 7458 | 8338 | 9322 | 10423 | 11653 | 13028 | 14566 |
253 | 8005 | 8949 | 10006 | 11187 | 12507 | 13983 | 15634 | 17479 | 19543 | 21849 |
379 | 12007 | 13424 | 15009 | 16780 | 18761 | 20975 | 23451 | 26219 | 29314 | 32774 |
568 | 18010 | 20136 | 22513 | 25170 | 28141 | 31463 | 35177 | 39329 | 43971 | 49161 |
852 | 27016 | 30204 | 33769 | 37755 | 42212 | 47194 | 52765 | 58993 | 65956 | 73741 |
1278 | 40523 | 45307 | 50654 | 56633 | 63318 | 70791 | 79147 | 88489 | 98934 | 110612 |
9.31 | 11.6 | 14.5 | 18.2 | 22.7 | 28.4 | 35.5 | 44.4 | 55.5 | 69.4 | |
0.01 | 1 | 1 | 1 | 1 | 2 | 2 | 2 | 2 | 2 | 3 |
0.02 | 1 | 2 | 2 | 2 | 2 | 3 | 3 | 3 | 4 | 4 |
0.02 | 2 | 2 | 3 | 3 | 3 | 4 | 4 | 5 | 5 | 6 |
0.03 | 3 | 4 | 4 | 5 | 5 | 6 | 6 | 7 | 8 | 9 |
0.05 | 5 | 5 | 6 | 7 | 8 | 9 | 10 | 11 | 12 | 13 |
0.08 | 7 | 8 | 9 | 10 | 11 | 13 | 14 | 16 | 18 | 20 |
0.11 | 11 | 12 | 14 | 15 | 17 | 19 | 22 | 24 | 27 | 30 |
0.17 | 17 | 18 | 21 | 23 | 26 | 29 | 32 | 36 | 40 | 45 |
0.26 | 25 | 28 | 31 | 35 | 39 | 43 | 48 | 54 | 61 | 68 |
0.38 | 37 | 42 | 46 | 52 | 58 | 65 | 73 | 81 | 91 | 102 |
0.58 | 56 | 62 | 70 | 78 | 87 | 97 | 109 | 122 | 136 | 152 |
0.86 | 84 | 94 | 105 | 117 | 131 | 146 | 163 | 183 | 204 | 228 |
1.3 | 126 | 140 | 157 | 175 | 196 | 219 | 245 | 274 | 306 | 343 |
2.0 | 188 | 210 | 235 | 263 | 294 | 329 | 368 | 411 | 460 | 514 |
2.9 | 282 | 316 | 353 | 395 | 441 | 493 | 552 | 617 | 689 | 771 |
4.4 | 424 | 474 | 530 | 592 | 662 | 740 | 827 | 925 | 1034 | 1156 |
6.6 | 635 | 710 | 794 | 888 | 993 | 1110 | 1241 | 1388 | 1551 | 1734 |
9.9 | 953 | 1066 | 1191 | 1332 | 1489 | 1665 | 1862 | 2081 | 2327 | 2602 |
14.8 | 1430 | 1598 | 1787 | 1998 | 2234 | 2498 | 2792 | 3122 | 3491 | 3903 |
22.2 | 2145 | 2398 | 2681 | 2997 | 3351 | 3746 | 4189 | 4683 | 5236 | 5854 |
33.3 | 3217 | 3597 | 4021 | 4496 | 5026 | 5620 | 6283 | 7025 | 7854 | 8781 |
49.9 | 4825 | 5395 | 6032 | 6744 | 7540 | 8429 | 9424 | 10537 | 11781 | 13171 |
74.8 | 7238 | 8092 | 9047 | 10115 | 11309 | 12644 | 14137 | 15805 | 17671 | 19757 |
112 | 10857 | 12138 | 13571 | 15173 | 16964 | 18966 | 21205 | 23708 | 26506 | 29635 |
168 | 16285 | 18208 | 20357 | 22760 | 25446 | 28449 | 31808 | 35562 | 39759 | 44452 |
253 | 24428 | 27312 | 30535 | 34139 | 38169 | 42674 | 47711 | 53343 | 59639 | 66679 |
379 | 36642 | 40967 | 45803 | 51209 | 57254 | 64011 | 71567 | 80014 | 89459 | 100018 |
568 | 54963 | 61451 | 68704 | 76814 | 85880 | 96017 | 107350 | 120021 | 134188 | 150027 |
852 | 82445 | 92176 | 103056 | 115220 | 128820 | 144026 | 161025 | 180032 | 201282 | 225040 |
1278 | 123668 | 138265 | 154584 | 172831 | 193231 | 216038 | 241538 | 270048 | 301923 | 337560 |
For a pressure coefficient Pcoef = 18.2 and steam flow = 592 kg/h - the flow factor Kv is 4.4.
The tables above are based on the formula:
Kv = m / (31.7 (dP / v)1/2) (1)
m= steam flow (kg/h)
dP = pressure drop (bar)
v = specific volume of steam before control valve (m3/kg)
Steam Kv calculator based on eq. 1:
Control Valve terminology, bodies, trim, flow characteristics, Cv and Kv sizing, noise, actuators and positioners
Instrumentation and process control systems - design and documentation.
Flow coefficients - Cv - for typical ball valves - reduced and full bore.
Control valves and cavitation, application ratio and multi stage control valves.
Flow capacities vs. stem opening.
Seat leakage classification through control valves.
Sizing control valves to match process requirements.
An online control valve - Cv - calculator for gases.
Steam consumption and condensate generation when heating liquid or gas flows
Calculate control valves in steam systems.
The valve authority expresses the ratio between pressure drop across the control valve compared to total pressure drop across the whole system.
Applications guide for selecting valves.
Sizing of water control valves - Imperial units.