Pressure drop | Water flow (kg/h) | |||||||||||
7200 | 10800 | 14400 | 18000 | 36000 | 72000 | 108000 | 144000 | 180000 | 360000 | 720000 | ||
(kPa) | (bar) | Water flow (kg/s) | ||||||||||
2 | 3 | 4 | 5 | 10 | 20 | 30 | 40 | 50 | 100 | 200 | ||
1 | 0.01 | 72.0 | 108 | 144 | 180 | 360 | 720 | 1080 | 1440 | 1800 | 3600 | 7200 |
2 | 0.02 | 50.9 | 76.4 | 102 | 127 | 254 | 509 | 763 | 1019 | 1273 | 2546 | 5091 |
3 | 0.03 | 41.6 | 62.4 | 83.1 | 103 | 207 | 415 | 623 | 831 | 1039 | 2078 | 4157 |
4 | 0.04 | 36.0 | 54.0 | 72.0 | 90.0 | 180 | 360 | 540 | 720 | 900 | 1800 | 3600 |
5 | 0.05 | 32.2 | 48.3 | 64.4 | 80.5 | 161 | 321 | 483 | 644 | 805 | 1610 | 3220 |
10 | 0.1 | 22.8 | 34.2 | 45.5 | 56.9 | 113 | 227 | 342 | 455 | 569 | 1138 | 2277 |
20 | 0.2 | 16.1 | 24.2 | 32.2 | 40.3 | 80.5 | 161 | 242 | 322 | 402 | 805 | 1610 |
30 | 0.3 | 13.2 | 19.7 | 26.3 | 32.9 | 65.7 | 131 | 197 | 263 | 329 | 657 | 1315 |
40 | 0.4 | 11.4 | 17.1 | 22.8 | 28.5 | 56.9 | 114 | 171 | 228 | 285 | 569 | 1138 |
50 | 0.5 | 10.2 | 15.3 | 20.4 | 25.5 | 50.9 | 102 | 153 | 204 | 255 | 509 | 1018 |
100 | 1 | 7.2 | 10.8 | 14.4 | 18.0 | 36.0 | 72.0 | 108 | 144 | 180 | 360 | 720 |
200 | 2 | 5.1 | 7.6 | 10.2 | 12.7 | 25.5 | 50.9 | 76.4 | 102 | 127 | 255 | 509 |
300 | 3 | 4.2 | 6.2 | 8.3 | 10.4 | 20.8 | 41.6 | 62.4 | 83.1 | 104 | 208 | 416 |
400 | 4 | 3.6 | 5.4 | 7.2 | 9.0 | 18.0 | 36.0 | 54.0 | 72.0 | 90.0 | 180 | 360 |
500 | 5 | 3.2 | 4.8 | 6.4 | 8.1 | 16.1 | 32.2 | 48.3 | 64.4 | 80.5 | 161 | 322 |
1000 | 10 | 2.3 | 3.4 | 4.6 | 5.7 | 11.4 | 22.8 | 34.2 | 45.5 | 56.9 | 114 | 228 |
2000 | 20 | 1.6 | 2.4 | 3.2 | 4.0 | 8.1 | 16.1 | 24.2 | 32.2 | 40.3 | 80.5 | 161 |
3000 | 30 | 1.3 | 2.0 | 2.6 | 3.3 | 6.6 | 13.2 | 19.7 | 26.3 | 32.9 | 65.7 | 131 |
4000 | 40 | 1.1 | 1.7 | 2.3 | 2.9 | 5.7 | 11.4 | 17.1 | 22.8 | 28.5 | 56.9 | 114 |
For a water control valve with
- the Kv value should be approximately 2.6 according the table above.
Kv can be calculated as:
Kv = q / (dp)1/2 (1)
Kv = Kv value
q = water flow (m3/h)
dp = pressure drop (bar)
Control Valve terminology, bodies, trim, flow characteristics, Cv and Kv sizing, noise, actuators and positioners
Instrumentation and process control systems - design and documentation.
Hot and cold water service systems - design properties, capacities, sizing and more.
Flow coefficients - Cv - for typical ball valves - reduced and full bore.
Typical flow coefficients - Cv - for butterfly valves.
Seat leakage classification through control valves.
Comparing flow coefficients Cv to flow factors Kv.
Calculate flow factor Kv for liquids, steam and gases - metric units.
Flow coefficients - Cv - and flow factors - Kv - for straight through diaphragm valves.
The valve authority expresses the ratio between pressure drop across the control valve compared to total pressure drop across the whole system.
Sizing of water control valves - Imperial units.
Typical flow coefficients - Cv - and flow factors - Kv - for weir diaphragm valves.