Condensate Pipes - Flash Steam Generated
In general condensate lines should be designed to handle start-up conditions with huge amounts of condensate generated from cold steam pipes and cold heating equipment. As a rule of thumb - the maximum condensate load at start up is often twice the maximum steam load during operation.
Sometimes, especially in high pressure steam systems with heavy load heat exchangers, generated flash steam may be the limitation of the condensate lines.
Flash steam generated can be calculated as
w% = 100 (hil - hfl ) / hfe (1)
w% = ratio of flash steam generated (%)
hil = initial liquid enthalpy (kJ/kg)
hfl = final liquid enthalpy (kJ/kg)
hfe = enthalpy of evaporation (kJ/kg)
The condensate load can be calculated as
wc = ws w% / 100 (2)
wc = condensate load (kg/h)
ws = steam flow rate (kg/h)
Example - Generated Flash Steam
The gauge pressure in a heat exchanger before the steam trap is 10 bar . The condensate lines and condensate receiver are vented so the gauge pressure is equal to 0 bar (atmospheric).
From the steam properties table :
hil = 781 kJ/kg, initial liquid enthalpy at 11 bar abs
hfl = 418 kJ/kg, final liquid enthalpy at 1 bar abs
hfe = 2258 kJ/kg, enthalpy of evaporation at 1 bar abs
The flash steam generated can be calculated as
w% = 100 ((781 kJ/kg) - (418 kJ/kg)) / (2258 kJ/kg)
= 16.1 %
If the steam flow rate through the heat exchanger is 200 kg/h - the condensate load can be calculated as
wc = (200 kg/h) (16.1 %) / 100
= 32 kg/h
• Flash Steam
Generation of flash steam in steam and condensate systems. Thermodynamic fundamentals, heat loss, energy recovery and more.
• Sizing of Steam and Condensate Pipes
Dimensions of steam and condensate pipe lines. Calculate pressure losses, recommended velocities, capacities and more.
Condensate Generated in Cold Steam Pipes - SI Units
Huge amounts of condensate are generated when cold steam pipes are heated up must be drained from the pipes.
Condensate Pipe Lines - Friction Resistance Imperial Units
Friction or major resistance in condensate pipe lines.
Condensate Pipe Lines - Sizing
Flow and pressure loss in condensate return lines - SI Units.
Flash Steam Energy Loss
When flash steam is generated and vented to the surroundings a considerable amount of energy is lost
Flash Steam Generation - Fundamental Physics
Tutorial to the basic physics behind flash steam generation
Flash Steam Generation - Imperial Units (psig)
When condensate passes steam traps - flash steam is generated.
Flash Steam Generation - SI-units
When condensate leaves the steam traps - flash steam is generated. Amount of flash steam generated at different pressures - kN/m2.
Insulated Steam Pipes - Condensate Generated
Heat loss from steam pipes generates condensate which must be drained from the system - imperial units.
Insulated Steam Pipes - Condensate Generated (kg/h per 100m)
Heat loss from steam pipes generates condensate which must be drained from the system.
Recommended Velocities in Steam Systems
The steam velocity in a steam distribution system should be within certain limits to avoid excessive wear and tear
Steam - Condensate Pipe Lines - Capacities (kW)
Maximum capacities for condensate pipe lines in kW steam consumption.
Steam - Gravity Return Condensate Pipes - Capacities
Max. capacities (lb/hour) in gravity condensate return lines.
Steam Flash Generation (bar)
The amount of flash steam generated depends on steam pressure and pressure in the condensate lines.
Thermodynamic Properties of Saturated Steam: Data & Charts in Bar
Saturated Steam Table with properties like boiling point, specific volume, density, specific enthalpy, specific heat and latent heat of vaporization.
Vapor and Steam
An introduction to vapor and steam.