Condensate Generated in Cold Steam Pipes - SI Units
When cold steam pipes are heated up huge amounts of condensate are generated and must be drained from the pipes. It is important that steam traps are designed to handle start-up loads.
The diagram and table below can be used to roughly estimate the load of warm-up condensate generated when a steam system is heated up.
Steam Pressure (bar) | Condensate Generation (kg/100 m) | |||||||||||||
Nominal Pipe Dimension (mm) | ||||||||||||||
50 | 65 | 80 | 100 | 125 | 150 | 200 | 250 | 300 | 350 | 400 | 450 | 500 | 600 | |
0 | 9.2 | 14.4 | 19 | 27 | 37 | 47 | 71 | 101 | 134 | 159 | 208 | 262 | 308 | 309 |
0.35 | 10 | 15.9 | 20.8 | 29 | 40 | 52 | 69 | 112 | 146 | 174 | 227 | 287 | 338 | 470 |
0.7 | 11.3 | 17.8 | 23.4 | 33 | 45 | 58 | 88 | 125 | 165 | 196 | 255 | 322 | 379 | 529 |
1 | 12.2 | 19.5 | 25.4 | 36 | 50 | 64 | 96 | 135 | 179 | 212 | 277 | 350 | 412 | 575 |
2.5 | 13.4 | 21.3 | 27.8 | 39 | 53 | 70 | 105 | 148 | 195 | 232 | 303 | 383 | 450 | 627 |
4 | 15.8 | 25.2 | 33 | 47 | 63 | 82 | 123 | 175 | 233 | 276 | 360 | 454 | 535 | 745 |
5.5 | 17.8 | 28 | 37 | 52 | 71 | 92 | 138 | 196 | 260 | 308 | 402 | 507 | 598 | 832 |
7 | 19.3 | 30.6 | 40 | 57 | 77 | 100 | 151 | 214 | 284 | 335 | 438 | 553 | 651 | 906 |
8.5 | 20.1 | 31.8 | 42 | 59 | 80 | 104 | 157 | 223 | 293 | 349 | 455 | 574 | 676 | 942 |
10 | 20.8 | 33.1 | 43 | 62 | 83 | 108 | 162 | 230 | 305 | 361 | 472 | 595 | 700 | 997 |
12 | 22.6 | 35.8 | 47 | 67 | 90 | 117 | 176 | 250 | 331 | 392 | 513 | 646 | 760 | 1059 |
14 | 24.2 | 38.2 | 50 | 71 | 96 | 125 | 189 | 267 | 353 | 418 | 546 | 689 | 811 | 1130 |
16 | 28.1 | 45 | 58 | 83 | 113 | 146 | 219 | 312 | 412 | 489 | 638 | 805 | 947 | 1320 |
20 | 36 | 55 | 74 | 108 | 150 | 205 | 312 | 463 | 637 | 764 | 981 | 1228 | 1503 | 1700 |
25 | 39 | 59 | 80 | 117 | 162 | 222 | 338 | 502 | 692 | 828 | 1065 | 1362 | 1631 | 2315 |
30 | 41.5 | 64 | 85 | 124 | 173 | 237 | 360 | 534 | 735 | 882 | 1134 | 1420 | 1763 | 2464 |
40 | 44.3 | 68 | 91 | 132 | 184 | 253 | 385 | 570 | 784 | 940 | 1210 | 1514 | 1852 | 2627 |
• Heat Loss and Insulation
Steam and condensate pipes - heat loss uninsulated and insulated pipes, insulation thickness and more.
• Steam and Condensate
Huge amounts of condensate are generated when cold steam pipes are heated up must be drained from the pipes.
Condensate Generated in Cold Steam Pipes - Sizing of Steam Traps
When cold steam pipes are heated up they generate huge amounts of condensate that must be drained away from the pipe through steam traps - in Imperial Units.
Condensate Pipe Lines - Friction Resistance Imperial Units
Friction or major resistance in condensate pipe lines.
Condensate Pipe Lines - Sizing
Flow and pressure loss in condensate return lines - SI Units.
Condensate Pipes - Flash Steam Generated
Calculate flash steam generation in condensate pipe lines.
Condensate Pumping
High temperatures and danger of impeller cavitation is the major challenge for condensate pumping in steam systems.
Insulated Steam Pipes - Condensate Generated
Heat loss from steam pipes generates condensate which must be drained from the system - imperial units.
Insulated Steam Pipes - Condensate Generated (kg/h per 100m)
Heat loss from steam pipes generates condensate which must be drained from the system.
Steam & Condensate Equations
Steam consumption and condensate generation when heating liquid or gas flows
Steam - Condensate Pipe Lines - Capacities (kW)
Maximum capacities for condensate pipe lines in kW steam consumption.
Steam - Gravity Return Condensate Pipes - Capacities
Max. capacities (lb/hour) in gravity condensate return lines.
Steam Pipes - Installation of Drip Legs
Properly draining steam pipes for condensate.
Steam Trap Selection Guide
Steam trap selection guide - Float & Thermostatic, Inverted Bucket, Bimetal Thermostatic, Impulse and Thermodynamic Disc steam traps.
Steam Traps - Safety Factors
Selection of steam traps and their safety factors.