Condensate Generated in Cold Steam Pipes - Sizing of Steam Traps
When cold steam pipes are heated up they generate huge amounts of condensate that must be drained away from the pipe. It is important that the steam traps are designed to handle the start up load.
The diagram and table below can be used as a roughly estimate of the warm-up condensate load generated when the steam system is heated up.
Steam Gauge Pressure (psi) | Warm-Up Condensate Load (lb/100 ft) | ||||||||
Pipe Size (inch) | |||||||||
2 | 2 1/2 | 3 | 4 | 5 | 6 | 8 | 10 | 12 | |
0 | 6.2 | 9.7 | 12.8 | 18.2 | 24.6 | 31.9 | 48 | 68 | 90 |
5 | 6.9 | 11 | 14.4 | 20.4 | 27.7 | 35.9 | 53 | 77 | 101 |
10 | 7.5 | 11.8 | 15.5 | 22 | 29.9 | 38.8 | 58 | 83 | 109 |
20 | 8.4 | 13.4 | 17.5 | 24.9 | 33.8 | 44 | 66 | 93 | 124 |
40 | 9.9 | 15.8 | 20.6 | 29.3 | 39.7 | 52 | 78 | 110 | 145 |
60 | 11 | 17.5 | 22.9 | 32.6 | 44 | 57 | 86 | 122 | 162 |
80 | 12 | 19 | 24.9 | 35.3 | 48 | 62 | 93 | 132 | 175 |
100 | 12.8 | 20.3 | 26.9 | 37.8 | 51 | 67 | 100 | 142 | 188 |
125 | 13.7 | 21.7 | 28.4 | 40 | 55 | 71 | 107 | 152 | 200 |
150 | 14.5 | 23 | 30 | 43 | 58 | 75 | 113 | 160 | 212 |
175 | 15.3 | 24.2 | 31.7 | 45 | 61 | 79 | 119 | 169 | 224 |
200 | 16 | 25.3 | 33.1 | 47 | 64 | 83 | 125 | 177 | 234 |
250 | 17.2 | 27.3 | 35.8 | 51 | 69 | 89 | 134 | 191 | 252 |
300 | 25 | 38.3 | 51 | 75 | 104 | 143 | 217 | 322 | 443 |
400 | 27.8 | 43 | 57 | 83 | 116 | 159 | 241 | 358 | 493 |
500 | 30.2 | 46 | 62 | 91 | 126 | 173 | 262 | 389 | 535 |
600 | 32.7 | 50 | 67 | 98 | 136 | 187 | 284 | 421 | 579 |
800 | 38 | 58 | 77 | 113 | 203 | 274 | 455 | 670 | 943 |
1000 | 45 | 64 | 86 | 126 | 227 | 305 | 508 | 748 | 1052 |
1200 | 52 | 72 | 96 | 140 | 253 | 340 | 566 | 833 | 1172 |
1400 | 62 | 79 | 106 | 155 | 280 | 376 | 626 | 922 | 1297 |
1600 | 71 | 87 | 117 | 171 | 309 | 415 | 62 | 1018 | 1432 |
1750 | 78 | 94 | 126 | 184 | 333 | 448 | 746 | 1098 | 1544 |
1800 | 80 | 97 | 129 | 189 | 341 | 459 | 764 | 1125 | 1584 |
This table is based on an ambient temperature of 70 oF. For an ambient temperature of 0 oF, the values should be increased with 15% at 1800 psi and up to 50% at 0 psi.
- 1 ft (foot) = 0.3048 m
- 1 psi (lb/in2) = 6,894.8 Pa (N/m2) = 6.895×10-2 bar
- 1 lb = 0.4536 kg
• Insulation and Heat Loss from Steam and Condesate Pipe Lines
Heat loss from uninsulated and insulated steam and condensate pipes and tanks. Calculate insulation thicknesses.
• Steam and Condensate
Air Conditioning - Cooling of Air and Condensate Generated
Water may condensate when air is cooled in air conditioning systems.
Condensate Generated in Cold Steam Pipes - SI Units
Huge amounts of condensate are generated when cold steam pipes are heated up must be drained from the pipes.
Condensate Pipe Lines - Friction Resistance Imperial Units
Friction or major resistance in condensate pipe lines.
Condensate Pipe Lines - Sizing
Flow and pressure loss in condensate return lines - SI Units.
Condensate Pumping
High temperatures and danger of impeller cavitation is the major challenge for condensate pumping in steam systems.
Flash Steam Generation - Fundamental Physics
Tutorial to the basic physics behind flash steam generation
Insulated Steam Pipes - Condensate Generated
Heat loss from steam pipes generates condensate which must be drained from the system - imperial units.
Insulated Steam Pipes - Condensate Generated (kg/h per 100m)
Heat loss from steam pipes generates condensate which must be drained from the system.
Steam & Condensate Equations
Steam consumption and condensate generation when heating liquid or gas flows
Steam - Condensate Pipe Lines - Capacities (kW)
Maximum capacities for condensate pipe lines in kW steam consumption.
Steam - Gravity Return Condensate Pipes - Capacities
Max. capacities (lb/hour) in gravity condensate return lines.
Steam Pipes - Installation of Drip Legs
Properly draining steam pipes for condensate.
Steam Trap Selection Guide
Steam trap selection guide - Float & Thermostatic, Inverted Bucket, Bimetal Thermostatic, Impulse and Thermodynamic Disc steam traps.
Steam Traps - Safety Factors
Selection of steam traps and their safety factors.