The heat released when condensing steam can be expressed as
Q = he M                        (1)
Q = quantity of heat released (kJ, Btu)
Ms = mass of condensing steam (kg, lb)
he = specific evaporation enthalpy of steam (kJ/kg, Btu/lb)
The heat transfer rate - or power - in a condensing steam flow can be expressed as
q = he ms                        (2)
q = heat transfer (kW, Btu/h)
ms = steam flow rate (kg/s, lb/h)
Example - Heat released when Condensing Steam
5 kg of steam with atmospheric pressure, temperature 100 oC and evaporation enthalpy 2257 kJ/kg is condensated. The heat transfer can be calculated as
Q = (2257 kJ/kg) (5 kg)
   = 11285 kJ
Example - Heat Transfer Rate - or Power - in a Condensing Steam Flow
The heat transfer rate in a condensing steam flow rate of 8 kg/h (0.0022 kg/s), atmospheric pressure and temperature 100 oC - can be calculated as
q = (2257 kJ/kg) (0.0022 kg/s)
  = 5 kJ/s (kW)
Thermodynamics
Carnot Cycle Efficiency
Energy Transfer Equation
Fluid energy transfer.
Heat Transfer Coefficients in Heat Exchanger Surface Combinations
Heat, Work and Energy
Heat vs. work vs. energy.
Heating Systems - Steam and Condensate Loads
Heating Water by Injecting Steam
Water can be heated by injecting steam.
Overall Heat Transfer Coefficient: Definitions, Values & Applications
Steam & Condensate Equations
Steam consumption and condensate generation when heating liquid or gas flows
Steam - Flow vs. kW Rating
Calculate steam flow rate vs. kW rating.
Steam and Vapor Enthalpy
Vapor and steam enthalpy, specific enthalpy of saturated liquid, saturated vapor and superheated vapor.
Steam Heating Air
Submerged Coils - Heat Transfer Coefficients
Heat transfer coefficients for steam and hot water coils submerged in oil tanks.
Superheated Steam - Enthalpy
Enthalpy of steam superheated to temperatures above it's boiling point.
Understanding Convective Heat Transfer: Coefficients, Formulas & Examples
Wet Steam - Enthalpy