Natural Draft - Air Flow Volume and Velocity
The temperature difference between the outside air and the inside air creates a "natural draft" forcing air to flow through the building.
The direction of the air flow depends on the temperature of the outside and inside air. If the inside air temperature is higher than the outside air temperature, the inside air density is less than the outside air density, and the inside air will flow up and out of the upper parts of the building. The colder outside air will flow in to the lower parts of the building.
If the outside air temperature is higher than the inside air temperature - the inside air is more dense than the outside air - and the air flows down inside in the building. Warmer outside air flows in to the upper parts of the building.
Natural Draft Head
The natural draft head can be calculated as
dh mmH2O = 1000 h (ρ o - ρ r ) / ρ h2o (1)
dh mmH2O = head in millimeter water column (mm H 2 O)
ρ o = density outside air (kg/m 3 )
ρ r = density inside air (kg/m 3 )
ρ h2o = density water (in general 1000 kg/m 3 )
h = height between outlet and inlet air (m)
Natural Draft Pressure
Equation (1) can be modified to SI pressure units:
dp = g ( ρ o - ρ r ) h                                   (1b)
d p = pressure (Pa, N/m 2 )
g = acceleration of gravity - 9.81 (m/s 2 )
Density and Temperature
With air density 1.293 kg/m 3 at 0 o C - the air density at any temperature can be expressed as
ρ = (1.293 kg/m 3 ) (273 K) / (273 K + t)                                                 (2)
or
ρ = 353 / (273 + t) (2b)
ρ = density of air (kg/m 3 )
t = the actual temperature ( o C)
Equation (1) above can easily be modified by replacing the densities with equation (2) .
Natural Draft Pressure Calculator
The calculator below can be used to calculate the natural draft pressure generated by the inside and outside temperature difference.
Major and Minor System Loss
The natural draft force will be balanced to the major and minor loss in ducts , inlets and outlets. The major and minor loss in the system can be expressed as
dp = λ (l / d h ) ( ρ r v 2 / 2) + Σξ 1/2 ρ r v 2 (3)
dp = pressure loss (Pa, N/m 2 , lb f /ft 2 )
λ = Darcy-Weisbach friction coefficient
l = length of duct or pipe (m, ft)
d h = hydraulic diameter (m, ft)
Σ ξ = minor loss coefficient (summarized)
Air Flow and Air Velocity
Equation (1) and (3) can be combined to express the air velocity through the duct
v = [(2 g ( ρ o - ρ r ) h ) / ( λ l ρ r / d h + Σ ξ ρ r )] 1/2 (4)
Equation (4) can also be modified to express the air flow volume through the duct
q = π d h 2 /4 [(2 g ( ρ o - ρ r ) h ) / ( λ l ρ r / d h + Σ ξ ρ r )] 1/2 (5)
q = air volume (m 3 /s)
Natural Draft Air Flow and Velocity Calculator
The calculator below can be used to calculate the air flow volume and velocity in a duct similar to the drawing above. The friction coefficient used is 0.019 which is appropriate for normal galvanized steel ducts.
Example - Natural Draft
Calculate the air flow caused by natural draft in a normal family house with two floors. The height of the hot air column from ground floor to outlet air duct above roof is approximately 8 m . The outside temperature is -10 o C and the inside temperature is 20 o C .
A duct of diameter 0.2 m goes from 1. floor to the outlet above the roof. The length of the duct is 3.5 m . Air leakages through the building are neglected. The minor coefficients are summarized to 1.
The density of the outside air can be calculated as
ρ o = (1.293 kg/m 3 ) (273 K) / ((273 K) + (-10 o C))
= 1.342 kg/m 3
The density of the inside air can be calculated as
ρ r = (1.293 kg/m 3 ) ( 273 K) / ((273 K) + (20 o C))
= 1.205 kg/m 3
The velocity through the duct can be calculated as
v = [(2 (9.81 m/s 2 ) ((1.342 kg/m 3 ) - (1.205 kg/m 3 )) (8 m)) / ( 0.019 (3.5m)(1.205 kg/m 3 )/(0.2 m) + 1 (1.205 kg/m 3 ) )] 1/2
= 3.7 m/s
The air flow can be calculated as
q = (3.7 m/s) 3.14 (0.2 m) 2 / 4
= 0.12 m 3 /s
Note!
that these equations can be used for dry air, not for mass flow and energy loss calculations where air humidity may have vast effects.
Natural Draft Chart - SI and Imperial Units
Ventilation
Air Curtains or Air Screens
Calculate air curtains or air screens in open doorways used to keep acceptable indoor comfort in buildings.
Chimney Sizing
Calculate chimney draft and required chimney area - online calculator.
Chimney's Size vs. Boiler Power
The size of chimney vs. boiler's heat load.
Chimneys and Fireplace Sizing
Chimneys and fireplaces for stoves burning wood or coal as fuel.
Colebrook Equation
Darcy-Weisbach Equation - Major Pressure and Head Loss due to Friction
Equivalent Length vs. Minor Pressure Head Loss in Pipe and Duct Components
Minor pressure and head loss in pipes vs. equivalent length in tubes and duct systems.
HVAC Ducts - Air Velocities
Recommended air velocities in HVAC ducts.
Infiltration - Heat Losses from Buildings
Estimated infiltration heat losses from buildings.
Stack or Flue Effect
The stack or flue effect occurs when the outdoor temperature is lower than indoor temperature.