Engineering ToolBox - Resources, Tools and Basic Information for Engineering and Design of Technical Applications!

Natural Draft - Air Flow Volume and Velocity

Air flow - volume and velocity - due to stack or flue effect caused by indoor hot and outdoor cold temperature difference.

The temperature difference between the outside air and the inside air creates a "natural draft" forcing air to flow through the building.

The direction of the air flow depends on the temperature of the outside and inside air. If the inside air temperature is higher than the outside air temperature, the inside air density is less than the outside air density, and the inside air will flow up and out of the upper parts of the building. The colder outside air will flow in to the lower parts of the building.

If the outside air temperature is higher than the inside air temperature - the inside air is more dense than the outside air - and the air flows down inside in the building. Warmer outside air flows in to the upper parts of the building.

natural draugt velocity volume flow

Natural Draft Head

The natural draft head can be calculated as

dhmmH2O = 1000 h (ρo - ρr) / ρh2o                   (1)

where

dhmmH2O = head in millimeter water column (mm H2O)

ρo = density outside air (kg/m3)

ρr = density inside air (kg/m3)

ρh2o = density water (in general 1000 kg/m3)

h = height between outlet and inlet air (m)

Natural Draft Pressure

Equation (1) can be modified to SI pressure units:

dp = g ( ρo - ρr) h                                   (1b)

where

d p = pressure (Pa, N/m2)

g = acceleration of gravity - 9.81 (m/s2)

Density and Temperature

With air density 1.293 kg/m 3 at 0 oC - the air density at any temperature can be expressed as

ρ = (1.293 kg/m3) (273 K) / (273 K + t)                               (2)

or

ρ = 353 / (273 + t) (2b)

where

ρ = density of air (kg/m3)

t = the actual temperature (oC)

Equation (1) above can easily be modified by replacing the densities with equation (2) .

Natural Draft Pressure Calculator

The calculator below can be used to calculate the natural draft pressure generated by the inside and outside temperature difference.

Major and Minor System Loss

The natural draft force will be balanced to the major and minor loss in ducts, inlets and outlets. The major and minor loss in the system can be expressed as

dp = λ (l / dh ) (ρr v2 / 2) + Σ ξ 1/2 ρr v2                    (3)

where

dp = pressure loss (Pa, N/m2, lbf/ft2)

λ = Darcy-Weisbach friction coefficient

l = length of duct or pipe (m, ft)

dh = hydraulic diameter (m, ft)

Σ ξ = minor loss coefficient (summarized)

Air Flow and Air Velocity

Equation (1) and (3) can be combined to express the air velocity through the duct

v = ((2 g ( ρo - ρr ) h) / ( λ l ρr / dh + Σ ξ ρr ))1/2                  (4)

Equation (4) can also be modified to express the air flow volume through the duct

q = π dh2 / 4 ((2 g (ρo - ρr ) h) / (λ l ρr / dh + Σ ξ ρr))1/2                   (5)

where

q = air volume (m3/s)

Natural Draft Air Flow and Velocity Calculator

The calculator below can be used to calculate the air flow volume and velocity in a duct similar to the drawing above. The friction coefficient used is 0.019 which is appropriate for normal galvanized steel ducts.

Example - Natural Draft

Calculate the air flow caused by natural draft in a normal family house with two floors. The height of the hot air column from ground floor to outlet air duct above roof is approximately 8 m. The outside temperature is -10 oC and the inside temperature is 20 oC .

A duct of diameter 0.2 m goes from 1. floor to the outlet above the roof. The length of the duct is 3.5 m. Air leakages through the building are neglected. The minor coefficients are summarized to 1.

The density of the outside air can be calculated as

ρo = (1.293 kg/m3) (273 K) / ((273 K) + (-10 oC))

= 1.342 kg/m3

The density of the inside air can be calculated as

ρr = (1.293 kg/m3) (273 K) / ((273 K) + (20 oC))

= 1.205 kg/m3

The velocity through the duct can be calculated as

v = ((2 (9.81 m/s2) ((1.342 kg/m3) - (1.205 kg/m3)) (8 m)) / (0.019 (3.5m)(1.205 kg/m3 ) / (0.2 m) + 1 (1.205 kg/m3)))1/2

= 3.7 m/s

The air flow can be calculated as

q = (3.7 m/s) 3.14 (0.2 m)2 / 4

= 0.12 m3/s

Note!

that these equations can be used for dry air, not for mass flow and energy loss calculations where air humidity may have vast effects.

Natural Draft Chart - SI and Imperial Units

Natural draft chart - imperial and metric units

3D Engineering ToolBox - draw and model technical applications! 2D Engineering ToolBox - create and share online diagram drawing templates! Engineering ToolBox Apps - mobile online and offline engineering applications!

Unit Converter


















































9.19.10

.
Cookie Settings