HVAC Ducts - Air Velocities
Flow velocity in air ducts should be kept within certain limits to avoid noise and unacceptable friction loss and energy consumption. Low velocity design is very important for the energy efficiency of the air distribution system. Doubling the duct diameter reduces the friction loss by factor 32.
Low and Medium Pressure Loss Ducts
- Maximum friction rate 0.1 - 0.2 inches W.G./100 ft
- Velocity 1500 - 2000 ft/min (8 - 10 m/s)
| Air Flow Rate | Maximum Velocity | ||
| (m3/h) | (CFM) | (m/s) | (ft/min) |
| < 300 | < 175 | 2.5 | 490 |
| < 1000 | < 590 | 3 | 590 |
| < 2000 | < 1200 | 4 | 785 |
| < 4000 | < 2350 | 5 | 980 |
| < 10000 | < 5900 | 6 | 1180 |
| > 10000 | > 5900 | 7 | 1380 |
High Pressure Loss Ducts
- Maximum friction rate less than 0.4 inches W.G./100 ft
- Velocity 2000 - 3500 ft/min (10 - 18 m/s)
Shafts
| < 5000 | < 2950 | 12 | 2350 |
| < 10000 | < 5900 | 15 | 2950 |
| < 17000 | < 10000 | 17 | 3350 |
| < 25000 | < 14700 | 20 | 3940 |
| < 40000 | < 23500 | 22 | 4300 |
| < 70000 | < 41000 | 25 | 4900 |
| < 100000 | < 59000 | 30 | 5800 |
It is common to keep main duct velocity above 20 m/s (3940 ft/min).
Corridors
| < 5000 | < 2950 | 10 | 2000 |
| < 10000 | < 5900 | 12 | 2350 |
| < 17000 | < 10000 | 15 | 2950 |
| < 25000 | < 14700 | 17 | 3350 |
| < 40000 | < 23500 | 20 | 3940 |
User Areas
- Offices, receptions, lounges and similar
| < 17000 | < 10000 | 14 | 2750 |
| < 25000 | < 14700 | 16 | 3150 |
Typical Air Velocity Guidelines
Low Velocity Duct Systems
- typical 400 - 2000 ft/min (2 - 10 m/s)
| Applications | Recommended max. Velocity (ft/min) | |||
| Main Ducts | Branch Ducts | |||
| Supply | Return | Supply | Return | |
| Apartments | 1000 | 800 | 600 | 600 |
| Banks | 2000 | 1500 | 1600 | 1200 |
| Hospital rooms | 1500 | 1300 | 1200 | 1000 |
| Apartments, Hotel rooms | 1500 | 1300 | 1200 | 1000 |
| Industrial | 3000 | 1800 | 2200 | 1500 |
| Libraries | 2000 | 1500 | 1600 | 1200 |
| Meeting rooms, cafeterias | 2000 | 1500 | 1600 | 1200 |
| Offices | 2000 | 1500 | 1600 | 1200 |
| Residences | 1000 | 800 | 600 | 600 |
| Restaurants, stores | 2000 | 1500 | 1600 | 1200 |
| Auditoriums, churches, cinemas, theaters | 1300 | 1100 | 1000 | 800 |
Medium Velocity Duct Systems
- typical 2000 - 2500 ft/min (10 - 12.5 m/s)
High Velocity Duct Systems
- typical 2500 - 3000 ft/min (12.5 - 15 m/s)
• Ventilation Systems
Air Ducts - Velocity Diagram
Air flow volume, duct size, velocity and dynamic pressure.
Duct Systems - Pressure Classifications
Duct systems are commonly divided into three pressure classifications.
Duct Velocity
Calculate velocities in circular and rectangular ducts - imperial and SI-units - online calculator.
Ductwork - Seal Classes
Ductwork air leakage classes.
Natural Draft - Air Flow Volume and Velocity
Air flow - volume and velocity - due to stack or flue effect caused by indoor hot and outdoor cold temperature difference.
Spiral Ducts - Dimensions
Standard dimensions of spiral ducts - Imperial units.
Velocity Classification of Ventilation Ducts
Recommended air velocities in ventilation ducts
Velocity Units Converter
Convert between speed and velocity units like m/s, km/h, knots, mph and ft/s.