Building Element | Heat-Transfer Coefficient U-value | ||
(Btu/(hr ft2 oF)) | (W/(m2K)) | ||
Doors | Single sheet - metal | 1.2 | 6.8 |
1 inch - wood | 0.65 | 3.7 | |
2 inches - wood | 0.45 | 2.6 | |
Roofing | Corrugated metal - uninsulated | 1.5 | 8.5 |
1 inch wood - uninsulated | 0.5 | 2.8 | |
2 inches wood - un-insulated | 0.3 | 1.7 | |
1 inch wood - 1 inch insulation | 0.2 | 1.1 | |
2 inch wood - 1 inch insulation | 0.15 | 0.9 | |
2 inches - concrete slab | 0.3 | 1.7 | |
2 inches - concrete slab - 1 inch insulation | 0.15 | 0.9 | |
Windows | Vertical single glazed window in metal frame | 5.8 | |
Vertical single glazed window in wooden frame | 4.7 | ||
Vertical double glazed window, distance between glasses 30 - 60 mm | 2.8 | ||
Vertical triple glazed window, distance between glasses 30 - 60 mm | 1.85 | ||
Vertical sealed double glazed window, distance between glasses 20 mm | 3.0 | ||
Vertical sealed triple glazed window, distance between glasses 20 mm | 1.9 | ||
Vertical sealed double glazed window with "Low-E" coatings | 0.32 | 1.8 | |
Vertical double glazed window with "Low-E" coatings and heavy gas filling | 0.27 | 1.5 | |
Vertical double glazed window with 3 plastic films ("Low-E" coated) and heavy gas filling | 0.06 | 0.35 | |
Horizontal single glass | 1.4 | 7.9 | |
Walls | 6 inches (150 mm) - poured concrete 80 lb/ft3 | 0.7 | 3.9 |
10 inches (250 mm) - brick | 0.36 | 2.0 |
U-value (or U-factor) is a measure of the rate of heat loss or gain through a construction of materials. The lower the U-factor, the greater the material's resistance to heat flow and the better is the insulating value. U-value is the inverse of R-value.
The overall U-value of a construction consisting of several layers can be expressed as
U = 1 / ∑ R (2)
U = heat transfer coefficient (Btu/hr ft2 oF, W/m2K)
R = "R-value" - the resistance to heat flow in each layer (hr ft2 oF/Btu, m2K/W)
The R-value of the single layer can be expressed as:
R = 1 / C = s / k (3)
C = layer conductance (Btu/hr ft2 oF, W/m2K)
k = thermal conductivity of layer material (Btu in/hr ft2 oF, W/mK)
s = thickness of layer (inches, m)
Note! - in addition to resistance in each construction layer - there is a resistance from the inner and outer surface to the surroundings. If you want to add the surface resistance to the U calculator below - use one - 1- for thickness - lt - and the surface resistance for the conductivity - K.
This calculator can be used to calculate the overall U-value for a construction with four layers. Add the thickness - lt - and the layer conductivity - K - for each layer. For fewer than four layers, replace the thickness of one or more layers with zero.
A concrete wall with thickness 0.25 (m) and conductivity 1.7 (W/mK) is used for the default values in the calculator above. The inside and outside surface resistance is estimated to 5.8 (m2 K/W).
The U value can be calculated as
U = 1 / (1 / (5.8 m2K/W) + (0.25 m) / (1.7 W/mK))
= 3.13 W/m2K
Material | Resistance R-value | |
(hr ft2 oF/Btu) | (m2K/W) | |
Wood bevel siding 1/2" x 8", lapped | 0.81 | 0.14 |
Wood bevel siding 3/4" x 10", lapped | 1.05 | 0.18 |
Stucco (per inch) | 0.20 | 0.035 |
Building paper | 0.06 | 0.01 |
Plywood 1/4" | 0.31 | 0.05 |
Plywood 3/8" | 0.47 | 0.08 |
Plywood 1/2" | 0.62 | 0.11 |
Hardboard 1/4" | 0.18 | 0.03 |
Softboard, pine or similar 3/4" | 0.94 | 0.17 |
Softboard, pine or similar 1 1/2" | 1.89 | 0.33 |
Softboard, pine or similar 2 1/2" | 3.12 | 0.55 |
Gypsum board 1/2" | 0.45 | 0.08 |
Gypsum board 5/8" | 0.56 | 0.1 |
Fiberglass 2" | 7 | 1.2 |
Fiberglass 6" | 19 | 3.3 |
Common brick per inch | 0.20 | 0.04 |
2 x 4 stud wall, uninsulated | 5 | 0.88 |
2 x 4 stud wall with 3 1/2" batt insulation | 15 | 2.6 |
2 x 4 stud wall with 1" polystyrene rigid board, 3 1/2" insulation blanket | 18 | 3.2 |
2 x 4 stud wall with 3/4" insulation board, 3 1/2" batt insulation, 5/8" polyurethane insulation | 22 | 3.9 |
2 x 6 stud wall with 5 1/2" insulation blanket | 23 | 4 |
2 x 6 stud wall with 3/4" insulation board, 5 1/2" batt insulation, 5/8" polyurethane insulation | 28 | 4.9 |
Heating systems - capacity and design of boilers, pipelines, heat exchangers, expansion systems and more.
Thermal resistance in building elements like walls, floors and roofs above and below the ground.
Heat flow thermal resistance of unfaced and faced duct wrap insulation.
Overall heat transfer loss from buildings - transmission, ventilation and infiltration.
Estimated infiltration heat losses from buildings.
Run, roof slope, gable height and gable area.
Steam radiators and steam convectors - heating capacities and temperature coefficients.
Calculate required number of studs in a wall.
Water condensation on inside glass windows surfaces vs. outside temperature and inside temperature and humidity.