Natural Gas Pipes - Low Pressure Capacities vs. Size
The tables below can be used for natural gas pipe sizing.
Steel Pipe - Schedule 40
| Pipe Size (in) | Capacity of Pipe (MBH ≈ CFH) | ||||||
| Pipe Length (ft) | |||||||
| Nominal | Inside diameter | 10 | 20 | 40 | 80 | 150 | 300 |
| 1/2 | 0.622 | 120 | 85 | 60 | 42 | 31 | 22 |
| 3/4 | 0.824 | 272 | 192 | 136 | 96 | 70 | 50 |
| 1 | 1.049 | 547 | 387 | 273 | 193 | 141 | 100 |
| 1 1/4 | 1.380 | 1200 | 849 | 600 | 424 | 310 | 219 |
| 1 1/2 | 1.610 | 1860 | 1316 | 930 | 658 | 480 | 340 |
| 2 | 2.067 | 3759 | 2658 | 1880 | 1330 | 971 | 686 |
| 2 1/2 | 2.469 | 6169 | 4362 | 3084 | 2189 | 1593 | 1126 |
| 3 | 3.068 | 11225 | 7938 | 5613 | 3969 | 2898 | 2049 |
| 4 | 4.026 | 23479 | 16602 | 11740 | 8301 | 6062 | 4287 |
| 5 | 5.047 | 42945 | 30367 | 21473 | 15183 | 11088 | 7841 |
| 6 | 6.065 | 69671 | 49265 | 34836 | 24632 | 17989 | 12720 |
| 8 | 7.981 | 141832 | 100290 | 70916 | 50145 | 36621 | 25895 |
- pressure less than 1 1/2 psig
- common to use fittings factor 1.5 - equivalent pipe length in table above = pipe length + 50%
- pressure drop 0.5 inches water column
- specific gravity of natural gas 0.6
- One MBH is equivalent to 1000 BTU's per hour (0.29 kW = 0.29 kJ/s)
- energy content in natural gas 1000 Btu/ft3(37.26 MJ/m3)
- steel pipes schedule 40
For natural gas the nominal BTU/ft3 varies from about 900 to 1100 BTU/ft3. In general it is common to set
- 1 Cubic Foot (ft3, CF) = Approx 1000 BTUs
- 1 CFH = 1 MBH (MBH is thousands of BTUs per hour)
Copper Tubing - type K
| Nominal | Outside Diameter | Inside Diameter | 10 | 20 | 40 | 80 |
| 1/4 | 3/8 | 0.305 | 15 | 10 | 7 | 5 |
| 3/8 | 1/2 | 0.402 | 33 | 24 | 17 | 12 |
| 1/2 | 5/8 | 0.527 | 74 | 52 | 37 | 26 |
| 5/8 | 3/4 | 0.652 | 138 | 97 | 69 | 49 |
| 3/4 | 7/8 | 0.745 | 203 | 143 | 101 | 72 |
| 1 | 1 1/8 | 0.995 | 469 | 332 | 235 | 166 |
| 1 1/4 | 1 3/8 | 1.245 | 894 | 632 | 447 | 316 |
- copper tubing type K
Copper Tubing - type L
| 1/4 | 3/8 | 0.315 | 16 | 11 | 8 | 6 |
| 3/8 | 1/2 | 0.430 | 41 | 29 | 20 | 14 |
| 1/2 | 5/8 | 0.545 | 81 | 58 | 41 | 29 |
| 5/8 | 3/4 | 0.666 | 146 | 103 | 73 | 52 |
| 3/4 | 7/8 | 0.785 | 236 | 167 | 118 | 84 |
| 1 | 1 1/8 | 1.025 | 511 | 362 | 256 | 181 |
| 1 1/4 | 1 3/8 | 1.265 | 936 | 662 | 468 | 331 |
- copper tubing type L
- 1 Btu/h = 0.293 W
- 1 lb = 0.4536 kg
- 1 ft (foot) = 0.3048 m
- 1 in water = 248.8 N/m2 (Pa) = 0.0361 lb/in2 (psi) = 25.4 kg/m2 = 0.0739 in mercury
- 1 psi (lb/in2) = 6,894.8 Pa (N/m2)
• Gases and Compressed Air
Gas Pipes - Approved Materials
Materials approved for gas pipes.
Gas Pipes - Low Pressure Sizing
Sizing gas pipes for apartment service lines.
House Gas Pipes - Capacities vs. Dimensions
Carrying capacity of house gas pipes - in imperial and metric units.
Methane Gas - Specific Heat vs. Temperature
Specific heat of Methane Gas - CH4 - at temperatures ranging 200 - 1100 K.
Natural Gas - Equipment Consumption
Natural gas consumption for equipment like boiling pans, ovens, cookers, kettles and more.
Natural Gas - Meter Capacities
Types of natural gas meters and their capacities.
Natural Gas - Pipe Sizing Calculator
Calculate capacities and dimensions of natural gas pipe lines.
Natural Gas Apartment Consumption vs. no. of Apartments
Multiple apartments and natural gas demand.
Natural Gas Laboratory Consumption vs. no. of Outlets
Natural gas consumption in laboratory outlets.
Natural Gas Pipes - Minimum Cover
Burial dept and minimum cover of underground natural gas pipes.
Natural Gas Piping - Sizing of Low Pressure Pipes vs. Capacity
Sizing low pressure natural gas pipe lines - Metric units.
Natural Gas Piping - Sizing vs. Capacity
Sizing natural gas pipes - pressures above 5 psi (35 kPa).
Orifices - Natural Gas Capacity
Capacity of natural gas orifices.