Heat Gain from Electrical Motors in Continuous Operation
Electrical motors in air condition systems contributes to the heat loads in air condition systems and will influence on the dimensions of cooling equipment.
Heat loads from electrical motors and fans in different locations can be estimated from the table below:
Shaft Output (kW) | Full Load Electrical Motor Efficiency - η - (%) | Electrical Motor Input (kW) | Location of Fan and Motor | ||
1 Motor and Fan in the Inlet Air Flow or in the Room (kW) | 2 Motor Outside the Air Flow or Outside the Room. The Fan in the Inlet Air Flow or in the Room (kW) | 3 Motor in the Room. The Fan in the Outlet Air Flow (kW) | |||
0.05 | 40 | 0.13 | 0.13 | 0.05 | 0.08 |
0.07 | 46 | 0.15 | 0.15 | 0.07 | 0.08 |
0.10 | 55 | 0.18 | 0.18 | 0.10 | 0.08 |
0.14 | 60 | 0.23 | 0.23 | 0.14 | 0.09 |
0.20 | 64 | 0.31 | 0.31 | 0.20 | 0.11 |
0.28 | 66 | 0.42 | 0.42 | 0.28 | 0.14 |
0.40 | 70 | 0.60 | 0.60 | 0.40 | 0.20 |
0.56 | 72 | 0.78 | 0.78 | 0.56 | 0.22 |
0.80 | 76 | 1.05 | 1.05 | 0.80 | 0.25 |
1.1 | 80 | 1.38 | 1.38 | 1.1 | 0.28 |
1.6 | 80 | 2.0 | 2.0 | 1.6 | 0.40 |
2.5 | 81 | 3.1 | 3.1 | 2.5 | 0.60 |
4.0 | 82 | 4.9 | 4.9 | 4.0 | 0.90 |
5.6 | 84 | 6.7 | 6.7 | 5.6 | 1.1 |
8.0 | 84 | 9.5 | 9.5 | 8.0 | 1.5 |
11.2 | 86 | 13.0 | 13.0 | 11.2 | 1.8 |
16 | 87 | 18.4 | 18.4 | 16 | 2.4 |
20 | 88 | 22.7 | 22.7 | 20 | 2.7 |
25 | 89 | 28.0 | 28.0 | 25 | 3.0 |
32 | 89 | 36.0 | 36.0 | 32 | 4.0 |
40 | 89 | 45.0 | 45.0 | 40 | 5.0 |
50 | 90 | 56.0 | 56.0 | 50 | 6.0 |
63 | 90 | 70.0 | 70.0 | 63 | 7.0 |
80 | 90 | 89.0 | 89.0 | 80 | 9.0 |
100 | 91 | 110 | 110 | 100 | 10.0 |
- 1 kW = 1000 Watts = 3412 Btu/h = 737.6 / 550 British hp = 1.341 British hp = 103/9.80665 kgf m/s = 737.6 ft lbf/s = 103/(9.80665 75) metric hp
• Air Conditioning Systems
Asynchronous Induction Motors - Electrical Properties
Typical electrical motor data like nominal current, fuse, start ampere, size of contactor and circuit breaker - for asynchronous induction motors.
Electric Motors - Efficiency
Electrical Motor Calculator: Power, Efficiency & Torque Calculations
Calculate amps, hp and kVA for electrical motors.
Electrical Motors - Heat Loss
Heat loss from an electrical motor to the surroundings.
Electrical Motors - Shaft Power vs. Voltage and Current
Calculate electric motors shaft power.
Heat Losses from Electrical Equipment
Heat loss from electrical equipment like switch-gear, transformers and variable frequency drives.