Asynchronous Induction Motors - Electrical Properties
The table below can used to determine electrical data for asynchronous 380 Voltage induction motors.
380 Voltage 50 Hz motors are commonly used in Europe. Note that the nominal voltage of existing 220/380 V and 240/415 V systems evolves toward the IEC recommended value of 230/400 V.
Rated PowerNominal current
- In -
(A)
Directly Fused
(A)
Star - Delta Started
(A)
Star - Delta contactor
- In -
(A)
Circuit Breaker
- In -
(A)
kWHP
0.2 0.3 0.7 2 2 16
0.33 0.5 1.1 2 2 16
0.5 0.7 1.4 2 2 16
0.8 1.1 2.1 4 4 16
1.1 1.5 2.6 4 4 16
1.5 2 3.6 6 4 (16) 22 16
2.2 3 5.0 10 6 (16) 22 16
3 4 6.6 16 10 (16) 22 16
4 5.5 8.5 20 16 (16) 22 16
5.5 7.5 11.5 25 20 (16) 22 16
7.5 10 15.5 35 25 (25) 22 25
11 15 22.2 35 35 (40) 30 40
15 20 30 50 35 (40) 30 40
22 30 44 63 50 (63) 60 60
30 40 57 80 63 (63) 60 60
45 66 85 125 100 90 100
55 75 104 160 125 110 100
75 100 140 200 160 150 200
90 125 168 225 200 220 200
110 150 205 300 250 220 200
132 180 245 400 300 300 400
160 220 290 430 300 300 400
200 270 360 500 430 480 400
240 325 430 630 500 480 480
Full-voltage, single-speed motor starters
Full-voltage starters (manual and magnetic) apply full voltage directly to motor terminals.
Reduced-voltage, single-speed motor starters
Some machines or loads may require a gentle start and smooth acceleration up to full speed.
Many starters apply reduced voltage to motor windings, primary resistor, primary reactor, autotransformer and solid state. Part winding and wye-delta starters can also provide reduced-voltage starting, although technically they are not reduced-voltage starters.
Motor Protection
Motors should have protection for themselves, in the branch circuit, and in the feeder line. Protection provided by fuses and circuit breakers guards against fault conditions caused by short circuits or grounds and over currents exceeding locked-rotor values.
Electrical
Electric Motors - Efficiency
Electrical Induction Motors - Torque vs. Speed
Full load operating torque vs. break down, pull up and locked rotor torque.
Electrical Motor Calculator: Power, Efficiency & Torque Calculations
Calculate amps, hp and kVA for electrical motors.
Electrical Motors - Shaft Power vs. Voltage and Current
Calculate electric motors shaft power.
Electrical Motors - Starting Devices
Direct-on-line starters, star-delta starters, frequency drives and soft starters.
Heat Gain from Electrical Motors in Continuous Operation
Amount of heat transferred from electrical motor to ambient room vs. locations of fan and motor.
Single and Three Phase AC - Electric Current vs. Power
Convert between single phase (120, 240 and 480 Voltage) and three phase (240 and 480 Voltage).
Variable Frequency Drives - Heat Loss and Required Air Cooling
Avoid overheated variable frequency drives with adequate ventilation.