Electric Circuits Voltage Drop
Voltage drop in an electric circuit can be calculated using Ohm's law as
U = R I (1)
U = voltage drop (volts, V)
R = electrical resistance in the electric circuit (ohms, Ω)
I = current (amps, A)
Example - Voltage Drop
Voltage drop in a 100 ft power line:
- 2×100 ft
- #10 copper
- electrical resistance 1.02 Ω /1000 ft
- current 10 amps
The electric resistance in the circuit can be calculated
R = (1.02 Ω/1000 ft) (2×100 ft)
= 0.204 Ω
The voltage drop in the circuit can be calculated with (1)
U = (0.204 Ω) (10 amps)
= 2.04 volts
Circular mils and Voltage drop
Voltage drop can also be calculated using mils like
U = K P L I / A (2)
K = specific resistivity (Ω - circular mils/foot)
P = phase constant = 2 (for single phase) = 1.732 (for three phase)
L = wire length (ft)
A = wire area ( circular mils)
Specific electric resistivity for different types of wire materials
- Solid Copper, K = 11 (temp 77 oF - 121 oF), K = 12 (temp 122 oF - 167 oF)
- Solid Aluminum, K = 18 (temp 77 oF - 121 oF), K = 20 (temp 122 oF - 167 oF)
- Stranded Copper, K = 11 (temp 77 oF - 121 oF), K = 12 (temp 122 oF - 167 oF)
- Stranded Aluminum, K = 19 (temp 77 oF - 121 oF), K = 20 (temp 122 oF - 167 oF)
Example - Specific resistivity and Voltage Drop
With values from the example above the voltage drop can be calculated as
U = (11 ohm - circular mils/foot) (2×100 ft) (10 A) / (10400 mils)
= 2.11 V
Copper Conductor - Voltage Drop Table
The voltage drop in a copper conductor can be estimated with
U = f I L (3)
f = factor from table below
I = current (amps)
L = conductor length (ft)
Size | Factor - f - | ||
AWG | Metric mm2 | ||
Single-phase | 3-phase | ||
14 | 2.08 | 0.476 | 0.42 |
12 | 3.31 | 0.313 | 0.26 |
10 | 5.26 | 0.196 | 0.17 |
8 | 8.37 | 0.125 | 0.11 |
6 | 13.3 | 0.0833 | 0.071 |
4 | 21.2 | 0.0538 | 0.046 |
3 | 0.0431 | 0.038 | |
2 | 33.6 | 0.0323 | 0.028 |
1 | 42.4 | 0.0323 | 0.028 |
1/0 | 53.5 | 0.0269 | 0.023 |
2/0 | 67.4 | 0.0222 | 0.020 |
3/0 | 85.0 | 0.019 | 0.016 |
4/0 | 107.2 | 0.0161 | 0.014 |
250 | 0.0147 | 0.013 | |
300 | 0.0131 | 0.011 | |
350 | 0.0121 | 0.011 | |
400 | 0.0115 | 0.009 | |
500 | 0.0101 | 0.009 |
• Electrical
Copper Wire - Electrical Resistance vs. Gauge
Gauge, weight, circular mils and electrical resistance in copper wire.
Electric Wire - Calculating Cross-Section Areas
Calculate single and bunched electric wire cross-section area and diameter.
Electric Wire - Maximum Length with 240 Volts Single-Phase Power
Maximum length of 240 V single phase electric wire with max. 2% voltage drop.
Electrical Motors - Maximum Cable Size and Length vs. Power
Maximum electrical motor cable length vs. power.
Electrical Voltage and Frequency Standards by Country
Typical voltages and frequencies used for domestic appliances in different countries.
Ohm's Law
The relation between voltage, current and electrical resistance.
Relative vs. Absolute Voltage
Electric circuits and voltage at any point.
Voltage Sources vs. Current Sources
Voltage and Current Sources