Electrical Motors - Maximum Cable Size and Length vs. Power
Three phase 230 V electrical motors and maximum cable length with 3% calculated voltage drop.
| Electric Motor Power | Maximum Cable Length (m, ft) | |||
| (kW) | (hk) | 30 (98) | 50 (164) | 100 (328) |
| Cable Size (mm2) | ||||
| 0.5 | 0.68 | 1.5 | 1.5 | 1.5 |
| 1 | 1.36 | 1.5 | 1.5 | 1.5 |
| 1.5 | 2.04 | 1.5 | 1.5 | 1.5 |
| 2 | 2.76 | 1.5 | 2.5 | 4 |
| 2.5 | 3.4 | 1.5 | 2.5 | 4 |
| 3 | 4.08 | 2.5 | 2.5 | 6 |
| 3.5 | 4.78 | 2.5 | 4 | 6 |
| 4 | 5.44 | 2.5 | 4 | 6 |
| 4.5 | 6.12 | 4 | 4 | 10 |
| 5 | 6.80 | 4 | 4 | 10 |
| 6 | 8.16 | 6 | 6 | 10 |
| 7 | 9.52 | 10 | 10 | 16 |
| 8 | 10.9 | 10 | 10 | 16 |
| 9 | 12.2 | 10 | 10 | 16 |
| 10 | 13.6 | 16 | 16 | 16 |
| 12 | 16.3 | 16 | 16 | 16 |
| 14 | 19.0 | 16 | 16 | 25 |
| 16 | 21.8 | 16 | 16 | 25 |
| 18 | 24.5 | 25 | 25 | 35 |
| 20 | 27.2 | 25 | 25 | 35 |
| 22 | 29.9 | 25 | 25 | 35 |
| 24 | 32.6 | 35 | 35 | 35 |
| 26 | 35.4 | 35 | 35 | 35 |
| 28 | 38.1 | 35 | 35 | 50 |
| 30 | 40.8 | 35 | 35 | 50 |
| 35 | 47.6 | 50 | 50 | 50 |
| 40 | 54.4 | 70 | 70 | 70 |
| 45 | 61.2 | 70 | 70 | 70 |
| 50 | 68 | 70 | 70 | 70 |
| 55 | 74.8 | 70 | 70 | 70 |
| 60 | 81.6 | 95 | 95 | 95 |
| 65 | 88.4 | 120 | 120 | 120 |
| 70 | 95.2 | 120 | 120 | 120 |
| 75 | 102 | 150 | 120 | 150 |
| 80 | 109 | 150 | 150 | 150 |
| 85 | 116 | 185 | 150 | 185 |
| 90 | 122 | 185 | 185 | 185 |
| 95 | 129 | 185 | 185 | 185 |
| 100 | 136 | 240 | 240 | 240 |
• Electrical
12 Volt - Amps Amps vs. Wire Gauge: Choosing the Right Wire Size
Maximum current (amps) in a 12V electrical circuit vs. size (AWG) and length of wire.
Electric Cable Size vs. Current Rating
Amps vs. cable size for fixed installations in buildings.
Electric Circuits Voltage Drop
Ohm's law and voltage drop in electric circuits.
Electric Motors - 230 & 460V Three Phase Circuits Wiring
Sizing of copper wire and transformers for three phase 230 & 460V electrical motors.
Electric Wire - Maximum Length with 240 Volts Single-Phase Power
Maximum length of 240 V single phase electric wire with max. 2% voltage drop.
Resistance vs. Resistivity
Electrical resistance and resistivity.
Three-Phase Electrical Motors - Power vs. Amps and Voltage
Full load amps, wire and conduit sizes for three phase electrical motors.