Electric Motors - 230 & 460V Three Phase Circuits Wiring
All wiring and electrical connections should comply with the National Electrical Code (NEC) and with local codes and practices.
Wire Gauge (AWG)
TransformerDistance - Motor to Transformer (Feet)
(HP)(volts)Apparent Power
(kVA)
100150200300500
1.5 230 3 12 12 12 12 10
2 460 3 12 12 12 12 12
3 230 3 12 12 12 10 8
3 230 5 12 10 10 8 6
3 460 5 12 12 12 12 10
5 230 7.5 10 8 8 6 4
5 460 7.5 12 12 12 10 8
7.5 230 10 8 6 6 4 2
7.5 460 10 12 12 12 10 8
10 230 15 6 4 4 4 1
10 460 15 12 12 12 10 8
15 230 20 4 4 4 2 0
15 460 20 12 10 10 8 6
20 230 1) 4 2 2 1 0
20 460 1) 10 8 8 6 4
25 230 1) 2 2 2 0 0
30 230 1) 2 1 1 0 0
30 460 1) 8 6 6 4 2
40 230 1) 1 0 0 0 0
50 230 1) 1 0 0 0 0
50 460 1) 4 4 2 2 0
30 230 1) 1 0 0 0 0
60 460 1) 4 2 2 0 0
75 230 1) 0 0 0 0 0
75 460 1) 4 2 2 0 0
1) The local power company should be consulted
  • 1 hp = 0.746 kW
  • 1 ft (foot) = 0.3048 m
If undersized wire is used between the motor and the power source, the starting and load carrying cap abilities of the motor will be limited.
Apparent Power is the power supplied to the electric circuit - typical from a power supplier to the grid - to cover the real and reactive power consumption in the loads
Electrical
Electrical units, amps and electrical wiring, wire gauge and AWG, electrical formulas and motors.
AWG - American Wire Gauge vs. Circular Mils
AWG vs. diameter mil, circular mil, diameter in mm and area in mm2.
Electrical Motors - Maximum Cable Size and Length vs. Power
Maximum electrical motor cable length vs. power.
Electrical Motors - Single Phase 230 V Circuit Wiring
Copper wire gage and transformer size for single phase 230 volts electrical motors.
PVDF - PolyVinylidene Fluoride Pipes - Supports
Maximum distance between PVDF pipe supports.