Sound Attenuation - Main Duct to Branch Ducts
When main ducts are split into branches the sound power level - Lw - is reduced according the size of the branch, or amount of air to the branch.
The sound attenuation from a main duct to a branched duct can be calculated as
dLN = 10 log(Ab / Am)                                  (1)
dLN = sound attenuation (dB)
Ab = branch area (m2, ft2)
Am = main duct area (m2, ft2)
The attenuation is indicated in the diagram below:
Example - Sound Attenuation from Main Duct to Branched Duct
In an example 20% of the air goes to the branch duct and 80% of the air goes further on in the main duct. The branch duct area is 20% of the main duct area before the branch and the main duct area after the branch is 80% of the main duct area before the branch.
The sound attenuation from the main duct to the branch duct can be calculated:
dLN_branch = 10 log((20%) / (100%))
     = 7 dB
The sound attenuation in the main duct can be calculated:
dLN_main_duct = 10 log((80%) / (100%))
     = 1 dB
Acoustics
Noise and Attenuation
Lined Sheet-Metal Ducts - Sound Attenuation
Noise attenuation in rectangular straight, lined, sheet metal ducts.
Sound - Attenuation and Speed vs. Sound Frequency and Air Humidity
The speed and attenuation of sound in moist air varies with sound frequency and air humidity.
Sound Attenuation - Duct split to Terminals
Estimating sound attenuation where ducts splits to terminals.
Sound Attenuation in Duct Elbows
Noise attenuation in duct elbows by reflected sound.
Sound Transmission through Duct Walls
Sound transmission from ducts to surrounding rooms.
Sound Transmission through Flanking Paths
Sound transmitted through duct walls, floors and ceilings.
Ventilation Systems - Acoustic Calculation Procedure
Acoustic noise calculation procedure HVAC systems.