Unlined Sheet-Metal Ducts - Sound Attenuation
Attenuation of sound in unlined sheet metal ducts at different frequencies are indicated below:
DuctAttenuation (dB/m duct)
Octave band center frequency (Hz)
63.512525050010002000
and higher
Round 100 - 300 mm 0.1 0.1 0.1 0 0 0
Round > 300 mm 0 0 0 0 0 0
Rectangular 150 x 150 mm 0.65 0.65 0.5 0.35 0.35 0.35
Rectangular 600 x 600 mm 0.65 0.65 0.35 0.15 0.15 0.15
Rectangular 1800 x 1800 mm 0.35 0.35 0.15 0.03 0.03 0.03
Example - Sound Attenuation in an Unlined Duct
The sound attenuation in a rectangular 600 x 600 mm unlined duct is 0.35 dB/m for frequency 250 Hz. The sound attenuation in 10 m duct is
(10 m) (0.35 dB/m) = 3.5 dB
Acoustics
Room acoustics and acoustic properties, decibel A, B and C, Noise Rating (NR) curves, sound transmission, sound pressure, sound intensity and sound attenuation.
Noise and Attenuation
Lined Sheet-Metal Ducts - Sound Attenuation
Noise attenuation in rectangular straight, lined, sheet metal ducts.
Sound Attenuation - Duct split to Terminals
Estimating sound attenuation where ducts splits to terminals.
Sound Attenuation in Duct Elbows
Noise attenuation in duct elbows by reflected sound.
Sound Attenuation in Ducts due to End Reflection
Low frequency noise transferred from main duct to end terminals is reflected back to main duct.
Sound Transmission through Duct Walls
Sound transmission from ducts to surrounding rooms.
Sound Transmission through Flanking Paths
Sound transmitted through duct walls, floors and ceilings.
Ventilation Systems - Acoustic Calculation Procedure
Acoustic noise calculation procedure HVAC systems.
Ventilation Systems - Classification of Noise Reduction Silencers
Noise in a ventilation system can be reduced by reactive, diffuser type, active and/or dissipative silencers.