Common Energy Recovery Principles

Heat recovery units used in ventilation and air condition systems are based on some common principles:

  • Return air
  • Rotating heat exchangers
  • Air-Fluid-Air exchangers
  • Cross flow exchangers
  • Heat pumps

Cross flow and rotating heat exchangers are illustrated below:

heat recovery efficiency

Return Air Recovery Units

In a return air recovery unit - used air is mixed into the make-up or supply air. Energy in outlet air is supplied directly into the make-up air. Both sensible and latent (moisture) heat is transferred.

Rotating Heat Exchangers

In a rotating heat exchanger - outlet air heats (or cools) the exchanger when the wheel passes through the outlet air flow. The energy is transferred to the make-up air when the wheel passes through the make-up air.

Both sensible and latent heat may be transferred. Latent heat when moisture in the outlet air condensates on the wheel. More moisture may be transferred using a hygroscopic wheel. For exchangers without hygroscopic wheels most of the condensate is drained out.

Air-Fluid-Air Exchangers

In an air-fluid-air heat recovery unit - heat is transferred in an heat exchanger from the outlet air to a circulating fluid. The fluid is circulated to a heat exchanger in the make-up air where the heat is transferred to the supply air.

Both sensible and latent heat may be transferred. Latent heat when moisture in the outlet air condensates in the heat exchanger. The moisture is not transferred.

Cross Flow Heat Exchangers

In a cross flow heat exchanger - heat is transferred directly from the outlet air to the make-up air through the separating walls in the heat exchanger.

Both sensible and latent heat may be transferred. Latent heat when moisture in the outlet air condensates on the heat exchanger. The moisture is not transferred.

Heat Pumps

A heat pump makes it possible - with some additional energy - to move more outlet air energy to the make-up air than any other system. The energy consumption is approximately 1/3 to 1/5 of the recovered energy.

Both sensible and latent heat may be transferred. Latent heat when moisture in the outlet air condensates on the heat exchanger. Moisture is not transferred.

Heating Process - Recovery without Moisture Transfer

The heating process without moisture transfer with a recovery unit - typical like the cross flow unit in the figure above - can be visualized in a psychrometric Mollier diagram as

Mollier diagram - Heating process without moisture transfer

Heating Process - Recovery with Moisture Transfer

The heating process with moisture transfer and a recovery unit - typical like the rotating wheel unit in the figure above - can be visualized in a psychrometric Mollier diagram as

Psychrometric Mollier diagram - Heat recovery with moisture transfer

The heating process with heat and moisture recovery can alternatively be visualized in a psychrometric chart as

Psychrometric chart - heating process with heat and moisture recovery

Temperature Transfer Efficiency

The temperature transfer efficiency for an heat recovery unit can be calculated as

μ t = (t2- t1 ) / (t3 - t1 ) (1)

where

μ t = temperature transfer efficiency

t1 = temperature in outside make-up air before the heat exchanger ( oC, oF)

t2 = temperature in outside make-up air after the heat exchanger ( oC, oF )

t3 = temperature in outlet air before the heat exchanger ( oC, oF )

Moisture Transfer Efficiency

The moisture transfer efficiency for an heat recovery unit can be calculated as

μm = (x2- x1 ) / (x3 - x1 ) (2)

where

μm = moisture transfer efficiency

x1 = moisture outside make-up air before the heat exchanger (kg/kg, grains/lb)

x2 = moisture outside make-up air after the heat exchanger (kg/kg, grains/lb )

x3 = moisture outlet air before the heat exchanger (kg/kg, grains/lb )

Enthalpy Transfer efficiency

The enthalpy transfer efficiency for an heat recovery unit can be calculated as

μ e = (h2- h1 ) / (h3 - h1 ) (3)

where

μ e = enthalpy transfer efficiency

h1 = enthalpy in outside make-up air before the heat exchanger (kJ/kg, Btu/lb)

h2 = enthalpy in outside make-up air after the heat exchanger (kJ/kg, Btu/lb )

h3 = enthalpy in outlet air before the heat exchanger (kJ/kg, Btu/lb )

Related Mobile Apps from The Engineering ToolBox Engineering Toolbox Apps

- free apps for offline use on mobile devices.

Heat Exchanger Efficiency Calculator

The calculator below can be used to calculate temperature, moisture or enthalpy efficiency for an heat exchanger - both Imperial and Metric units. The heat (kW) exchanged calulation is valid for metric units.

moisture ( kg/kg, grains/lb ) or enthalpy ( kJ/kg, Btu/lb ))

Related Topics

  • Air Psychrometrics

    Moist and humid air calculations. Psychrometric charts and Mollier diagrams. Air-condition systems temperatures, absolute and relative humidities and moisture content in air.
  • Ventilation Systems

    Design of systems for ventilation and air handling - air change rates, ducts and pressure drops, charts and diagrams and more.

Related Documents

Search

Search is the most efficient way to navigate the Engineering ToolBox.

Engineering ToolBox - SketchUp Extension - Online 3D modeling!

3D Engineering ToolBox Extension to SketchUp - add parametric components to your SketchUp model

Add standard and customized parametric components - like flange beams, lumbers, piping, stairs and more - to your Sketchup model with the Engineering ToolBox - SketchUp Extension - enabled for use with older versions of the amazing SketchUp Make and the newer "up to date" SketchUp Pro . Add the Engineering ToolBox extension to your SketchUp Make/Pro from the Extension Warehouse !

Translate this Page

Translate this page to Your Own Language .

About the Engineering ToolBox!

Privacy Policy

We don't collect information from our users. More about

We use a third-party to provide monetization technologies for our site. You can review their privacy and cookie policy here.

You can change your privacy settings by clicking the following button: .

Citation

This page can be cited as

  • The Engineering ToolBox (2003). Heat Recovery Efficiency. [online] Available at: https://www.engineeringtoolbox.com/heat-recovery-efficiency-d_201.html [Accessed Day Month Year].

Modify the access date according your visit.

3D Engineering ToolBox - draw and model technical applications! 2D Engineering ToolBox - create and share online diagram drawing templates! Engineering ToolBox Apps - mobile online and offline engineering applications!

Unit Converter

















































5.8.12

.