Engineering ToolBox - Resources, Tools and Basic Information for Engineering and Design of Technical Applications!

Air Heating Systems

Air heating buildings - heat supply vs. air flow and temperature.

Air heating systems may be cost effective if they can be made simple or if they can be combined with a ventilation system. But - be aware that due to the low specific heat of air the use of air for heating purposes is very limited. Larger heat loads requires large volumes of air resulting in huge oversized ducts and fans. Transport of huge volumes of air requires a lot of energy.

Required Air Volume in an Air Heating System

air heating system

Required air flow rate in an air heating system can be calculated as

L = Q / (cp ρ (t h - t r ))                                         (1)

where

L = air flow rate (m3 /s)

Q = heat loss covered by the air heating system (kW)

cp = specific heat air - 1.005 (kJ/kg oC)

ρ = density of air - 1.2 (kg/m3 )

t h = heating air temperature (oC)

t r = room temperature (oC)

As a rule of thumb the air heating supply temperature should be in the range 40-50 oC . The air flow should be in the range 1-3 times the room volume.

Equation (1) expressed in imperial units:

L = Q / (1.08 (t h - t r ))                                        (2)

where

Q = heat (btu/hr)

L = air volume (cfm)

t h = heating air temperature ( oF)

t r = room temperature ( oF)

Online Air Heating Calculator

Air Heating - Temperature Rise Diagram

The diagrams below are calculated from the equations above and can be used to estimate heat required to rise temperature in air flows.

SI units - kW, m3 /s and oC

air heating temperature kw diagram

Imperial units - Btu/h, cfm and oF

Air heating temperature btu/h diagram

  • 1 m3 /s = 3,600 m3/h = 35.32 ft3 /s = 2,118.9 ft3 /min (cfm)
  • 1 kW (kJ/s) = 859.9 kcal/h = 3,413 Btu/h
  • T(oC) = 5/9[T( oF) - 32]

Example - Heating a single room with air

A building with a large room with a heat loss 20 kW is heated with air with a maximum temperature 50 oC . The room temperature is 20 oC . The required air flow rate can be calculated as

L = (20 kW) / ((1.005 kJ/kg oC) (1.2 kg/m3 ) ((50 oC) - (20 oC)))

= 0.55 m3 /s

Required Air Flow from an Electric Furnace - Imperial Units

Required air flow from an electric furnace can be expressed in Imperial units as

L cfm = P w 3.42 / 1.08 dt                                   (3)

where

L cfm = required air flow (cfm)

P w = electric power (watts)

dt = temperature difference ( o F)

Related Topics

  • Heating Systems

    Design of heating systems - capacities and design of boilers, pipelines, heat exchangers, expansion systems and more.
  • Ventilation Systems

    Design of systems for ventilation and air handling - air change rates, ducts and pressure drops, charts and diagrams and more.

Related Documents

Search

Search is the most efficient way to navigate the Engineering ToolBox.

Engineering ToolBox - SketchUp Extension - Online 3D modeling!

3D Engineering ToolBox Extension to SketchUp - add parametric components to your SketchUp model

Add standard and customized parametric components - like flange beams, lumbers, piping, stairs and more - to your Sketchup model with the Engineering ToolBox - SketchUp Extension - enabled for use with older versions of the amazing SketchUp Make and the newer "up to date" SketchUp Pro . Add the Engineering ToolBox extension to your SketchUp Make/Pro from the Extension Warehouse !

Translate this Page

Translate this page to Your Own Language .

About the Engineering ToolBox!

Privacy Policy

We don't collect information from our users. More about

We use a third-party to provide monetization technologies for our site. You can review their privacy and cookie policy here.

You can change your privacy settings by clicking the following button: .

Citation

This page can be cited as

  • The Engineering ToolBox (2008). Air Heating Systems. [online] Available at: https://www.engineeringtoolbox.com/air-heating-systems-d_1136.html [Accessed Day Month Year].

Modify the access date according your visit.

3D Engineering ToolBox - draw and model technical applications! 2D Engineering ToolBox - create and share online diagram drawing templates! Engineering ToolBox Apps - mobile online and offline engineering applications!

Unit Converter

















































5.3.10

.