Pollution Concentration in Rooms
The concentration of a pollution in a limited space as a room, container, tank etc. depends on
- amount of polluted material spread in the room or space
- amount of fresh supply air or fluid
- the outlet positions and constructions
- the principles used for supply and outlet from the space
- fluid flow in the space
The generic equation for pollution concentration (amount of polluting product to amount of fluid in space (like air a room)) can be calculated
c = q / n V (1 - e-nt) + (c1 - c2) e-nt + c2 (1)
c = concentration in the space (or in the room) at perfect mix (m3/m3) (kg/kg)
q = amount of pollution added to the space (m3/h) (kg/h)
n = volume changes per hour (h-1)
V = volume or mass of the space (m3) (kg)
e = the number 2.72..
t = time (h)
c1 = concentration in the space at start (m3/m3) (kg/kg)
c2 = concentration in the supply fluid (m3/m3) (kg/kg)
If the start concentration (t = 0) of the space and the concentration in the supply fluid is zero, equation (1) can be reduced to
c = q / n V (1 - e-nt) (2)
Note! After some time the concentration in the room will stabilize. The table below shows the value of c when the amount of pollution q = 1, and the volume of the space V = 1.
Volume changes per hour (1/h) | Concentration of pollution - c - (m3/m3) (kg/kg) | ||||||||
Time - t - (min) | |||||||||
10 | 20 | 40 | 80 | 160 | 320 | 640 | 1280 | 2560 | |
0.5 | 0.1599 | 0.3070 | 0.5669 | 0.9732 | 1.4728 | 1.8610 | 1.9903 | 2.0000 | 2.0000 |
1 | 0.1535 | 0.2835 | 0.4866 | 0.7364 | 0.9305 | 0.9952 | 1.0000 | 1.0000 | 1.0000 |
2 | 0.1417 | 0.2433 | 0.3682 | 0.4653 | 0.4976 | 0.5000 | 0.5000 | 0.5000 | 0.5000 |
4 | 0.1216 | 0.1841 | 0.2326 | 0.2488 | 0.2500 | 0.2500 | 0.2500 | 0.2500 | 0.2500 |
8 | 0.0921 | 0.1163 | 0.1244 | 0.1250 | 0.1250 | 0.1250 | 0.1250 | 0.1250 | 0.1250 |
16 | 0.0582 | 0.0622 | 0.0625 | 0.0625 | 0.0625 | 0.0625 | 0.0625 | 0.0625 | 0.0625 |
32 | 0.0311 | 0.0312 | 0.0312 | 0.0313 | 0.0313 | 0.0313 | 0.0313 | 0.0313 | 0.0313 |
64 | 0.0156 | 0.0156 | 0.0156 | 0.0156 | 0.0156 | 0.0156 | 0.0156 | 0.0156 | 0.0156 |
• Ventilation Systems
Air Contaminants - Exposure Limits
Exposure limits for various air contaminants.
Air Intakes and Outlets
Ventilation systems - air intakes and outlets - rules of thumbs.
Carbon Dioxide Concentration in Rooms Occupied with People
Carbon dioxide concentration in a room may indicate air quality and ventilation system efficiency.
Design of Ventilation Systems
Design procedure for ventilation systems - air flow rates, heat and cooling loads, air shifts according occupants, air supply principles.
Outdoor Supply Air Rates
Recommended supply air rates of outdoor air - with or without smoking - in rooms like banks, assembly halls, hotels and many more.
Recommended Air Change Rates for Different Room Types
Fresh air (make up air) rquirements - or recommended air change rates (ACH) for typical rooms and buildings like auditoriums, kitchens, churches and more.