Water Evaporator and Condenser Equations
Total heat load:
h = c p ρ q dt
= 500 q dt                                          (1)
h = heat load (Btu/h)
c p = 1 (Btu/lb m o F) for water
ρ = 8.33 (lb m /gal) for water
q = water volume flow rate (gal/min)
dt = temperature difference ( o F)
Evaporator water flow rate can be expressed as
q evap = 24 h evap / dt                                         (2)
q evap = evaporator water flow rate (gallons per minute - gpm)
h evap = air condition load ( 1 refrigeration ton = 1 TONS cond = 12,000 Btu /h = 200 Btu/min = 3,025.9 k Calories /h = 12,661 kJ/h = 3517 kJ/s = 3517 kW = 4713 HP )
Condenser water flow rate can be expressed as
q cond = 30 h cond / dt                                         (3)
q cond = condenser water flow rate (gallons per minute - gpm)
h cond = air condition load, chiller tonnage ( 1 cooling tower ton = 1 TONS evap = 1 TONS cond x 1.25 = 15,000 Btu/h = 3,782 k Calories/h = 15,826 kJ/h )
Air Conditioning
Calculating Cooling Loads
Calculating chiller and cooling tower refrigeration loads - in tons.
Chilled Water Systems
Chilled water system equations - evaporator and condenser flow rates.
Cooling Power vs. Airflow and Duct Sizes
Typical relations between cooling power (tons cooling), air flow and duct size
Refrigeration Machinery - Required Ventilation
Ventilation required for refrigeration machinery and compressors in hot areas.