Fan Inlets - Air Density vs. Suction Pressure
If the inlet suction pressure of a fan exceeds 270 mm W.G (10 in W.G) the reduced air density should be compensated by increasing the suction pressures with a correction factor:
Suction Pressure (Water Gauge) | Pressure Correction Factor - f - | |
(mm) | (in) | |
-135 | -5 | 1.01 |
-200 | -7.5 | 1.02 |
-270 | -10 | 1.03 |
-380 | -14 | 1.04 |
-490 | -18 | 1.05 |
-600 | -22 | 1.06 |
- 1 in water = 248.8 N/m2= 0.0361 lb/in2 = 25.4 kg/m2 = 0.0739 in mercury
For suction pressures below 270 mm W.G (10 in W.G) the correction is normally neglected.
Corrected suction pressure can be expressed as:
Psc = Ps f (1)
Psc = corrected suction pressure (mm W.G., in W.G)
f = correction factor
Ps = design (and measured) suction pressure (mm W.G., in W.G)
Example - Correcting Suction Pressure
Design or measured suction pressure for a fan is Ps = -380 mm W.G. (-14 in W.G). The correction factor from table above 1.04. For a proper fan selection the suction pressure should be corrected to
Psc = (-380 mm W.G) 1.04
= -395 mm W.G.
• Ventilation Systems
Fan Capacity Diagrams
Pressure, head, air flow volume and fan capacity diagrams.
Fans - Capacity Control
How to modulate fans and their capacities.
Pumps and Fans - Energy Equation and Head Rise
The energy equation can be used to calculate the head rise in pumps and fans.