Ventilation Dampers - Classification
Classification by Function
Dampers may be classified according their functional tasks in the ventilation system:
  • adjustment
  • closing, running
  • closing, smoke
  • closing, fire
  • overpressure
  • modulating
Classification by Construction
  • plates
  • membranes
Classification by Leakage Class
  • based on BS EN 1751:1999
The leakage class determines the acceptable air leakage through the damper with a 100 Pa pressure difference.
  • class 0 - No requirements
  • class 1 - less than 0.2 m3/s per m2 valve area
  • class 2 - less than 0.04 m3/s per m2 valve area
  • class 3 - less than 0.008 m3/s per m2 valve area
  • class 4 - less than 0.0015 m3/s per m2 valve area
The air flow rates through the dampers at 100 Pa are in general available from the manufacturers catalogs.
FunctionClass
1 2 3
Adjustment x
Closing, running x
Closing, smoke x
Closing, fire x
Overpressure x
Modulation x
Calculating Leakage Air Flow Rate through a Closed Damper
The leakage air flow through a closed damper can be calculated if the the difference pressure through the damper and the leakage air flow rate at 100 Pa (manufacturer data) through the damper is known:
ql = q100 (dpl / 100)1/2                           (1)
ql = actual volume flow per m2 valve area (m3/s / m2)
q100 = volume flow at 100 Pa per m2 valve area (m3/s / m2)
dpl = actual pressure drop through the valve (Pa)
Ventilation
HVAC Dampers - Pressure Loss
Pressure head loss in HVAC dampers.
Ventilation Components - Minor Pressure Loss
Pressure loss in ventilation system components like dampers, filters, heaters, coolers and more.