Saturated Steam - Properties vs. Pressure - psi
Gauge Pressure
(psig)
Temperature
(oF)
Specific Volume Saturated Vapor
(ft3/lb)
Enthalpy
Saturated Liquid
(Btu/lb)
Evaporated
(Btu/lb)
Saturated Vapor
(Btu/lb)
25
(Inches Mercury Vacuum)
134 142 102 1017 1119
20
(Inches Mercury Vacuum)
162 73.9 129 1001 1130
15
(Inches Mercury Vacuum)
179 51.3 147 990 1137
10
(Inches Mercury Vacuum)
192 39.4 160 982 1142
5
(Inches Mercury Vacuum)
203 31.8 171 976 1147
0 1) 212 26.8 180 970 1150
1 215 25.2 183 968 1151
2 219 23.5 187 966 1153
3 222 22.3 190 964 1154
4 224 21.4 192 962 1154
5 227 20.1 195 960 1155
6 230 19.4 198 959 1157
7 232 18.7 200 957 1157
8 233 18.4 201 956 1157
9 237 17.1 205 954 1159
10 239 16.5 207 953 1160
12 244 15.3 212 949 1161
14 248 14.3 216 947 1163
16 252 13.4 220 944 1164
18 256 12.6 224 941 1165
20 259 11.9 227 939 1166
22 262 11.3 230 937 1167
24 265 10.8 233 934 1167
26 268 10.3 236 933 1169
28 271 9.85 239 930 1169
30 274 9.46 243 929 1172
32 277 9.1 246 927 1173
34 279 8.75 248 925 1173
36 282 8.42 251 923 1174
38 284 8.08 253 922 1175
40 286 7.82 256 920 1176
42 289 7.57 258 918 1176
44 291 7.31 260 917 1177
46 293 7.14 262 915 1177
48 295 6.94 264 914 1178
50 298 6.68 267 912 1179
55 300 6.27 271 909 1180
60 307 5.84 277 906 1183
65 312 5.49 282 901 1183
70 316 5.18 286 898 1184
75 320 4.91 290 895 1185
80 324 4.67 294 891 1185
85 328 4.44 298 889 1187
90 331 4.24 302 886 1188
95 335 4.05 305 883 1188
100 338 3.89 309 880 1189
105 341 3.74 312 878 1190
110 344 3.59 316 875 1191
115 347 3.46 319 873 1192
120 350 3.34 322 871 1193
125 353 3.23 325 868 1193
130 356 3.12 328 866 1194
135 358 3.02 330 864 1194
140 361 2.92 333 861 1194
145 363 2.84 336 859 1195
150 366 2.74 339 857 1196
155 368 2.68 341 855 1196
160 371 2.6 344 853 1197
165 373 2.54 346 851 1197
170 375 2.47 348 849 1197
175 377 2.41 351 847 1198
180 380 2.35 353 845 1198
185 382 2.29 355 843 1198
190 384 2.24 358 841 1199
195 386 2.19 360 839 1199
200 388 2.14 362 837 1199
205 390 2.09 364 836 1200
210 392 2.05 366 834 1200
215 394 2 368 832 1200
220 396 1.96 370 830 1200
225 397 1.92 372 828 1200
230 399 1.89 374 827 1201
235 401 1.85 376 825 1201
240 403 1.81 378 823 1201
245 404 1.78 380 822 1202
250 406 1.75 382 820 1202
255 408 1.72 383 819 1202
260 409 1.69 385 817 1202
265 411 1.66 387 815 1202
270 413 1.63 389 814 1203
275 414 1.6 391 812 1203
280 416 1.57 392 811 1203
285 417 1.55 394 809 1203
290 418 1.53 395 808 1203
295 420 1.49 397 806 1203
300 421 1.47 398 805 1203
305 423 1.45 400 803 1203
310 425 1.43 402 802 1204
315 426 1.41 404 800 1204
320 427 1.38 405 799 1204
325 429 1.36 407 797 1204
330 430 1.34 408 796 1204
335 432 1.33 410 794 1204
340 433 1.31 411 793 1204
345 434 1.29 413 791 1204
350 435 1.28 414 790 1204
355 437 1.26 416 789 1205
360 438 1.24 417 788 1205
365 440 1.22 419 786 1205
370 441 1.2 420 785 1205
375 442 1.19 421 784 1205
380 443 1.18 422 783 1205
385 445 1.16 424 781 1205
390 446 1.14 425 780 1205
395 447 1.13 427 778 1205
400 448 1.12 428 777 1205
450 460 1 439 766 1205
500 470 0.89 453 751 1204
550 479 0.82 464 740 1204
600 489 0.74 475 728 1203
650 497 0.69 483 719 1202
700 505 0.64 491 710 1201
750 513 0.6 504 696 1200
800 520 0.56 512 686 1198
900 534 0.49 529 666 1195
1000 546 0.44 544 647 1191
1250 574 0.34 580 600 1180
1500 597 0.27 610 557 1167
1750 618 0.22 642 509 1151
2000 636 0.19 672 462 1134
2250 654 0.16 701 413 1114
2500 669 0.13 733 358 1091
2750 683 0.11 764 295 1059
3000 696 0.08 804 213 1017
3206.22) 705.40 - - - -

1) Atmospheric pressure is used for the table except for 2)

2) Critical Point - At 3206.2 psia and 705.40 oF the vapor and liquid are indistinguishable. No change of state occurs when pressure increases above the critical point or when heat is added. At the critical point it is no longer referred to water or steam and it is not possible keep the water and steam apart.

  • 1 psi (lbf/in2) = 6894.8 Pa (N/m2) =  0.06895 bar

Note! Gauge Pressure = Absolute Pressure - Atmospheric Pressure

NTP - Normal Temperature and Pressure - is defined as 20oC (293.15 K, 68oF) and 1 atm ( 101.325 kN/m2, 101.325 kPa, 14.7 psia, 0 psig, 30 in Hg, 760 torr)

  • Vacuum steam is the general term used for saturated steam at temperatures below 100°C.

Example - Boiling Water at 212 oF and 0 psig

At atmospheric pressure - 0 psig - water boils at 212 oF. 180 Btu/lb of energy is required to heat 1 lb of water to saturation temperature 212 oF.

Therefore, at 0 psig and 212 oF - the specific enthalpy of water is 180 Btu/lb.

Another 970 Btu/lb of energy is required to evaporate the 1 lb of water at 212 oF to steam at 212 oF. Therefore, at 0 psig - the specific enthalpy of evaporation is 970 Btu/lb.

The total specific enthalpy of the steam (or heat required to evaporate water to steam) at atmospheric pressure and 212 oF can be summarized to

hs = (180 Btu/lb) + ( 970 Btu/lb)

    =  1150 Btu/lb

Saturated steam - saturated and evaporated enthalpy vs. steam pressure

Related Topics

  • Flash Steam

    Generation of flash steam in steam and condensate systems. Thermodynamic fundamentals, heat loss, energy recovery and more.
  • Sizing of Steam and Condensate Pipes

    Dimensions of steam and condensate pipe lines. Calculate pressure losses, recommended velocities, capacities and more.
  • Steam and Condensate

    Design of steam & condensate systems with properties, capacities, sizing of pipe lines, system configuration and more.
  • Thermodynamics

    Calculate heat, work, temperature and energy. The thermodynamics of steam and condensate systems. Water and Ice properties.

Related Documents

Search

Search is the most efficient way to navigate the Engineering ToolBox.

Engineering ToolBox - SketchUp Extension - Online 3D modeling!

3D Engineering ToolBox Extension to SketchUp - add parametric components to your SketchUp model

Add standard and customized parametric components - like flange beams, lumbers, piping, stairs and more - to your Sketchup model with the Engineering ToolBox - SketchUp Extension - enabled for use with older versions of the amazing SketchUp Make and the newer "up to date" SketchUp Pro . Add the Engineering ToolBox extension to your SketchUp Make/Pro from the Extension Warehouse !

Translate this Page

Translate this page to Your Own Language .

About the Engineering ToolBox!

Privacy Policy

We don't collect information from our users. More about

We use a third-party to provide monetization technologies for our site. You can review their privacy and cookie policy here.

You can change your privacy settings by clicking the following button: .

Citation

This page can be cited as

  • The Engineering ToolBox (2003). Saturated Steam - Properties - Imperial Units. [online] Available at: https://www.engineeringtoolbox.com/saturated-steam-properties-d_273.html [Accessed Day Month Year].

Modify the access date according your visit.

3D Engineering ToolBox - draw and model technical applications! 2D Engineering ToolBox - create and share online diagram drawing templates! Engineering ToolBox Apps - mobile online and offline engineering applications!

Unit Converter

















































5.8.12

.