Control Valves - Cavitation
Control valves and cavitation, application ratio and multi stage control valves.
According the Bernoulli equation - when a fluid pass a valve seat and the fluid velocity increase - the fluid pressure decrease.
Cavitation
If the speed through the valve is increases enough, the pressure in the fluid drops to a level where the fluid may start to boil, bubble or flash. And when the pressure recovers sufficiently the bubbles will collapse upon themselves. This collapse causes cavitation.
Control valves - flowstream pressure and cavitation
Cavitation may be noisy but is usually of low intensity and low frequency. This situation is extremely destructive and may wear out the trim and body parts of a valve in short time.
Application Ratio
A common way to characterize potential cavitation condition is the "applications ratio" (or "the incipient cavitation index") which can be expressed as
AR = pi - po / (pi - pv)                                (1)
AR = Application Ratio
pi = inlet pressure, absolute
po = outlet pressure, absolute
pv = vapor pressure of the fluid, absolute
For application ratios above 1 - the fluid flashes. This is not the same as cavitation, but the closer the ratio is to 1, the higher is the potential for cavitation.
Note! - the risk of cavitation increases with fluid temperature.
Example - Flashing Water
If we know the boiling point and the absolute pressure of a fluid (Steam Table with saturated steam properties) the minimum outlet pressure from a valve to avoid flashing can be calculated.
For an application ratio like one (AR = 1), equation (1) can modified to
AR = 1
or transformed to
po = pv
Using the "Steam Table" with saturated steam properties we can conclude that
  • for a water temperature of 17.51 oC and absolute inlet pressure of 1 bar - the minimum outlet pressure is 0.02 bar to avoid flashing
  • for a water temperature of 81.35 oC and absolute inlet pressure of 1 bar - the minimum outlet pressure is 0.5 bar to avoid flashing
  • For a water temperature of 99.63 oC and absolute inlet pressure of 1 bar - the minimum outlet pressure is 1 bar to avoid flashing
Note! Flashing is not the same as cavitation. Due to local conditions in a valve cavitation may start on much higher outlet pressures.
Multi Stage Control Valves
Cavitation can be avoided by using more than one control valve or more convenient - a multistage control valve.
Cavitation in multi stage control valves - fluid pressure along flow stream
As illustrated above the "vena contracta" is much lower in a single stage valve than in a multi stage valve. Depending on the pressure drop and the temperature of the fluid its possible to avoid cavitation conditions using more than one stage in a valve.
  • Control Valve Sizing
  • The Engineering ToolBox (2003). Control Valves - Cavitation. [online] Available at: https://www.engineeringtoolbox.com/control-valves-cavitation-d_490.html [Accessed Day Month Year].