Hot Water Expansion Tanks - Sizing

Required hot water expansion volume in open, closed and diaphragm tanks.

Expansion tanks are required in heating, cooling or air condition system to avoid unacceptable increases of system pressures when water expands during heat-up.

Explosive Power of Super-heated Water

  • 1 lb (0.45 kg) of nitroglycerin > 2 000 000 ft lbf (2 700 000 J)
  • 1 lb (0.45 kg) of water flashed into steam > 750 000 ft lbf (100 000 J)

Water - temperature rise and pressure rise in a closed system

Expansion tanks are in general designed as

  • open tanks
  • closed compression tanks
  • diaphragm tanks

Net expansion volume of water when heated can be expressed as

V net = (v1 / v0 ) - 1                                      (1)

V net = expansion volume of water ( ft3, m3 )

v0 = specific volume of water at initial (cold) temperature (ft3 /lb, m3 /kg)

v1 = specific volume of water at operating (hot) temperature (ft3 /lb, m3 /kg)

Open Expansion Tanks

Open expansion tanks

Required volume of an open expansion tank can be expressed as

V et = k V w [(v1 / v0 ) - 1]                                     (2)

V et = required expansion tank volume (gallon, liter)

k = safety factor (approximately 2 is common)

V w = water volume in the system (gallon, liter)

v0 = specific volume of water at initial (cold) temperature (ft3 /lb, m3 /kg)

v1 = specific volume of water at operating (hot) temperature (ft3 /lb, m3 /kg)

Note that in an open expansion tank fresh air is constantly absorbed in the water and tends to corrode the system. Open expansion tanks must also be located above the highest heating element, in general on the top of buildings, where they may be exposed to freezing.

Water - temperature volume expansion diagram

Closed Compression Expansion Tanks

Closed compression tanks can be designed as

  • adjustable expansion tanks - air is evacuated or injected by automatic valves to the tanks to control system pressures when temperature and expansion of water rises or falls
  • pump-pressured cushion tanks - water is evacuated or injected to the systems to compensate for temperature rise or fall
  • compression tanks with closed gas volumes - the tanks contains specific volumes of gas which is compressed when temperatures and system volumes increase

Water - Closed expansion tanks

Required volume in a closed expansion tank

V et = k V w [( v1 / v0 ) - 1] / [( p a / p0 ) - ( p a / p1 )]                                          (3)

where

p a = atmospheric pressure - 14.7 (psia)

p0 = system initial pressure - cold pressure (psia)

p1 = system operating pressure - hot pressure (psia)

Water - closed expansion tank sizing diagram

  • initial temperature 50 oF
  • initial pressure 10 psig
  • maximum operating pressure 30 psig

Diaphragm Expansion Tanks

Required volume in a diaphragm expansion tank

V et = k V w [( v1 / v0 ) - 1] / [1 - ( p0 / p1 )]                                            (4)

Water - diaphragm exspansion tank sizing diagram

  • initial temperature 50 oF
  • initial pressure 10 psig
  • maximum operating pressure 30 psig
  • safety factor aprox. 2
  • acceptance factor aprox. 0.5

Example - Volume in Open Expansion Tank

A system with 1000 gallons of water is heated from 68 oF to 176 oF .

Minimum expansion volume in an open expansion tank with a safety factor 2 can be calculated as

V et = 2 (1000 gallons) [((0.01651 ft3 /lb) / (0.01605 ft3 /lb)) - 1]

= 57 (gallons)

Related Topics

  • Heating Systems

    Design of heating systems - capacities and design of boilers, pipelines, heat exchangers, expansion systems and more.

Related Documents

Search

Search is the most efficient way to navigate the Engineering ToolBox.

Engineering ToolBox - SketchUp Extension - Online 3D modeling!

3D Engineering ToolBox Extension to SketchUp - add parametric components to your SketchUp model

Add standard and customized parametric components - like flange beams, lumbers, piping, stairs and more - to your Sketchup model with the Engineering ToolBox - SketchUp Extension - enabled for use with older versions of the amazing SketchUp Make and the newer "up to date" SketchUp Pro . Add the Engineering ToolBox extension to your SketchUp Make/Pro from the Extension Warehouse !

Translate this Page

Translate this page to Your Own Language .

About the Engineering ToolBox!

Privacy Policy

We don't collect information from our users. More about

We use a third-party to provide monetization technologies for our site. You can review their privacy and cookie policy here.

You can change your privacy settings by clicking the following button: .

Citation

This page can be cited as

  • The Engineering ToolBox (2005). Hot Water Expansion Tanks - Sizing. [online] Available at: https://www.engineeringtoolbox.com/expansion-tanks-d_885.html [Accessed Day Month Year].

Modify the access date according your visit.

3D Engineering ToolBox - draw and model technical applications! 2D Engineering ToolBox - create and share online diagram drawing templates! Engineering ToolBox Apps - mobile online and offline engineering applications!

Unit Converter

















































5.8.12

.