Engineering ToolBox - Resources, Tools and Basic Information for Engineering and Design of Technical Applications!

Ventilation Systems - Acoustic Calculation Procedure

Acoustic noise calculation procedure HVAC systems.

An acoustic noise calculation of a ventilation system can follow the procedure indicated in the example below:

Sound and Noise Sources

Estimate all sound power sources.

1. Estimate the Sound Power Level from the Fan - LN

Enter the manufacturer's sound power data or calculate the fan sound power.

2. Add Safety factors

Add safety factors - 3 dB is recommended.

Attenuation

Estimate the attenuation in the system.

10. Room and terminal effect

The sound pressure levels - Lp - are converted to sound power level - Lw - at the terminals. The acoustic characteristics of the room as well as the number and location of the terminals must be considered.

a) Determine the acoustic characteristics of the room. In this example an average sound absorption for the room is used.

b) Determine whether the receiver are in the direct or reverberant field. In the example the listener is approximately 1.5 m from the terminal.

c) Find the rooms absorption characteristics. In the example the absorption for the walls, ceiling, floor, persons, curtains and their areas, is calculated to 30 m2 Sabine. According a) and c) the attenuation is 8 dB.

d) Determine how many terminals the listener are influenced by. Note! Remember to include supply and return fans. In the example the listener are influenced by two terminals. From c) we subtract 3 dB.

The attenuation from the terminal to the room is 5 dB. The values are entered in the example.

11. Allowance for end reflection

In the example the duct dimension is 250 mm. Attenuation due to end reflection is entered below.

12. Duct work attenuation

Calculate the attenuation in unlined and lined ducts. Note that the table and diagrams list the attenuation in dB/m.

13. Elbow attenuation

Duct elbow - sound attenuation

Calculate the attenuation in the elbows.

14. Power-level split, branch to terminals

Ventilation ducts -  Sound Power Level Split

Determine the allowance for split - branch to terminals.

15. Power-level split, main duct to branch duct

Determine the allowance for split - main duct to branch.

16. Other attenuation

Add attenuation from other components.

Calculate Resulting Sound Power and Required additional Attenuation

20. Resulting Sound Power Fan

Subtract summarized attenuation from the fan sound power - inclusive safety factors

21. Sound pressure level criterion

Determine the sound pressure level criteria. This table indicates acceptable levels at different locations. Check against domestic rules.

In the example below Noise Rating - NR30 - is used as a criterion. NR-values are entered in line 1.

22. Silencer requirements

The silencer must be selected to provide the necessary attenuation. Manufacturer's data are preferred.

Example - Acoustic Calculation of a Ventilation System

You can save and modify your own copy of the example if you are signed into your Google Account.

Acoustic calculation of a ventilation system - example

Related Topics

  • Acoustics

    Room acoustics and acoustic properties. decibel A, B and C calculations. Noise Rating (NR) curves. Sound transmission through walls. Calculate sound pressure, sound intensity and sound attenuation.
  • HVAC Systems

    Design and sizing of Heating, Ventilation and Air Conditioning systems.
  • Noise and Attenuation

    Noise is usually defined as unwanted sound - noise, noise generation, silencers and attenuation in HVAC systems.

Related Documents

Search

Search is the most efficient way to navigate the Engineering ToolBox.

Engineering ToolBox - SketchUp Extension - Online 3D modeling!

3D Engineering ToolBox Extension to SketchUp - add parametric components to your SketchUp model

Add standard and customized parametric components - like flange beams, lumbers, piping, stairs and more - to your Sketchup model with the Engineering ToolBox - SketchUp Extension - enabled for use with older versions of the amazing SketchUp Make and the newer "up to date" SketchUp Pro . Add the Engineering ToolBox extension to your SketchUp Make/Pro from the Extension Warehouse !

Translate this Page

Translate this page to Your Own Language .

About the Engineering ToolBox!

Privacy Policy

We don't collect information from our users. More about

We use a third-party to provide monetization technologies for our site. You can review their privacy and cookie policy here.

You can change your privacy settings by clicking the following button: .

Citation

This page can be cited as

  • The Engineering ToolBox (2003). Ventilation Systems - Acoustic Calculation Procedure. [online] Available at: https://www.engineeringtoolbox.com/accoustic-calculation-ventilation-d_70.html [Accessed Day Month Year].

Modify the access date according your visit.

3D Engineering ToolBox - draw and model technical applications! 2D Engineering ToolBox - create and share online diagram drawing templates! Engineering ToolBox Apps - mobile online and offline engineering applications!

Unit Converter

















































5.8.12

.