Low Pressure Steam Safety Valves - Capacities

Sizing safety valves after boiler output power in low pressure systems (kW and Btu/hr).

The main purpose of a safety valve is to prevent the pressure in a system to exceed the certification pressure. Above certification pressure, no one can guaranty the systems safety - and especially for a steam system with very hot gas with huge amount of latent heat, the consequences can be dramatically.

The size of the safety valve depends primarily on the maximum boiler output and the operation pressure of the system. The safety valve shall as minimum have the evacuation capacity of all the vapor the boiler can produce running at full power at working (or certification) pressure.

The table below can be used to select a typical safety valve based on boiler output. Before final design, always consult the manufactures documentation.

Low Pressure Steam Safety Valves - Capacities
Pipe Size
DN
CapacityMaximum Boiler Output
(in)(mm)(kg/h)(lb/h)(kW)(Btu/h)
1/2 15 38 86 23 81 270
3/4 20 82 185 50 174 825
1 25 145 324 89 306 180
1 1/4 32 249 557 152 526 365
1 1/2 40 360 807 220 762 615
2 50 536 1 199 328 1 133 055
2 1/2 65 901 2 012 551 1 901 340
3 80 1 244 2 779 761 2 626 155
4 100 2 397 5 355 1 465 5 060 475

Note! The table above is based on low pressure steam of 100 kN/m2 (1 bar) or 15 psi in imperial units. Latent heat of saturated steam is 2201 kJ/kg (945 Btu/lb).

  • 1 N/m2 = 1 Pa = 1.4504 x 10-4 lb/in2 (psi) = 10-5 bar
  • For higher pressure, steam is compressed and require less volume - required size of the valve reduced
  • For lower pressure, steam is expanded and require more volume - required size of the valve increased

Capacity of low pressure steam safety valves chart

Related Topics

Related Documents

Search

Search is the most efficient way to navigate the Engineering ToolBox.

Engineering ToolBox - SketchUp Extension - Online 3D modeling!

3D Engineering ToolBox Extension to SketchUp - add parametric components to your SketchUp model

Add standard and customized parametric components - like flange beams, lumbers, piping, stairs and more - to your Sketchup model with the Engineering ToolBox - SketchUp Extension - enabled for use with older versions of the amazing SketchUp Make and the newer "up to date" SketchUp Pro . Add the Engineering ToolBox extension to your SketchUp Make/Pro from the Extension Warehouse !

Translate this Page

Translate this page to Your Own Language .

About the Engineering ToolBox!

Privacy Policy

We don't collect information from our users. More about

We use a third-party to provide monetization technologies for our site. You can review their privacy and cookie policy here.

You can change your privacy settings by clicking the following button: .

Citation

This page can be cited as

  • The Engineering ToolBox (2003). Low Pressure Steam Safety Valves - Capacities. [online] Available at: https://www.engineeringtoolbox.com/steam-safety-valves-d_107.html [Accessed Day Month Year].

Modify the access date according your visit.

3D Engineering ToolBox - draw and model technical applications! 2D Engineering ToolBox - create and share online diagram drawing templates! Engineering ToolBox Apps - mobile online and offline engineering applications!

Unit Converter

















































4.26.8

.