Spring Operated Safety Valves in Liquid Systems
Calculate spring operated relief valves in liquid systems.
Relief safety valve
The minimum discharge area of a spring operated relief safety valve in a liquid system can be calculated as
A = q SG1/2 / (28.14 Kbp Kvisc dp1/2)                                    (1)
A = discharge area (Square Inches)
q = relieving capacity (Gallons per Minute)
SG =Specific Gravity of the fluid
Kbp = capacity correction for back pressure - 1.0 for atmospheric pressure systems
Kvisc = correction factor due to velocity - 1.0 for most water systems
dp = differential pressure - set pressure (psig) + over pressure (psig) - back pressure (psig)