Velocity Pressure Head
Dynamic pressure or velocity head.
The dynamic pressure in a fluid flow can be expressed as
p d = 1/2 ρf v 2           (1)
p d = dynamic pressure in fluid (Pa, psf (lb/ft2))
ρf = density of fluid (kg/m3, slugs /ft3 )
v = fluid velocity (m/s, ft/s)
  • 1 Pa = 10-6 N/mm2= 10 -5 bar = 0.1020 kp/m2= 1.02x10-4 m H2O = 9.869x10-6 atm = 1.45x10-4 psi (lbf/in2)
  • 1 psf (lbf /ft2) = 47.88 N/m2(Pa) = 0.006944 lbf /in2(psi)
Head loss as water column can be calculated by dividing the dynamic pressure with the specific weight of water like
h w = p d / γw
= ( 1/2 ρf v2) / ( ρw g)
= ρf v2/ (2 ρw g)                  (2)
hw = head water (m Water, ft Water)
γw = ρw g = specific weight water (9807 N/m3, 62.4 l bf /ft3 )
ρw = density of water (1000 kg/m3, 1.940 slugs/ft3 )
g = acceleration of gravity ( 9.81 m/s2, 32.174 ft/s2)
Water Flow
If the flowing fluid is water - then ρf = ρ w , and (2) can be modified to
h w = v2/ 2 g             (3)
Or simplified to
Metric Units
hw (m H2O) = 0.051 v2            (3b)
hw (mm H2O) = 51 v2            (3c)
v = velocity (m/s)
Imperial Units
hw (ft H2O) = 0.0155 vfps 2            (3d)
hw (in H2O) = 0.186 vfps 2          (3e)
vfps = velocity (ft/s)
or
hw (ft H2O) = 0.0155 (v fpm / 60)2              (3f)
hw (in H2O) = 0.186 (v fpm / 60)2            (3g)
v fpm = velocity (ft/min)
Water Flow - Head to Velocity Calculator
This calculator can be used to calculate water velocity in a pipe or water stream from a measured head of water column. The dynamic pressure as head is typically measured with a pitot tube .
Water Flow - Velocity and Dynamic Head Chart
Air Flow - Velocity and Head
Water Flow - Velocity Heads
Velocity Heads vs. water Flow Velocities
Water Flow Velocity
- v -
(ft/sec)
Velocity Head
- h w -
(ft H2O)
0.5 0.004
1.0 0.016
1.5 0.035
2.0 0.062
2.5 0.097
3.0 0.140
3.5 0.190
4.0 0.248
4.5 0.314
5.0 0.389
5.5 0.470
6.0 0.560
6.5 0.657
7.0 0.762
7.5 0.875
8.0 0.995
8.5 1.123
9.0 1.259
9.5 1.403
10.0 1.555
11.0 1.881
12.0 2.239
13.0 2.627
14.0 3.047
15.0 3.498
16.0 3.980
17.0 4.493
18.0 5.037
19.0 5.613
20.0 6.219
21.0 6.856
22.0 7.525
  • 1 ft (foot) = 0.3048 m = 12 inches = 0.3333 yd
Air Flow
Metric Units
If the flowing fluid is air with ρf = 1.205 kg/m3 (20 oC) and the reference fluid is water with ρw = 1000 kg/m3 - (2) can be simplified to
hw (m H2O) = ((1.205 kg/m3 ) v2) / (2 ( 1000 kg/m3 ) 9.81 m/s2)
= 6.1 10 -5 v2              (4)
v = air velocity (m/s)
or
h w (mm H2O) = 6.1 10-2 v2              (4b)
Note! - these simplified equations must be relaculated for other air temperatures and densities .
Imperial Units
h w (ft H2O) = (v / C)2/ 12                                   (4c)
h w (in H2O) = (v / C)2                  (4c)
v = velocity (ft/min)
C = constant (4005 for temperature 70 oF)
The constant C and temperature:
Constant C vs. Air Temperatures
Air Temperature
( oF)
C
35 3872
40 3891
45 3910
50 3932
55 3952
60 3970
65 3987
70 4005
75 4025
80 4045
85 4064
90 4081
95 4101
100 4117
150 4298
Air Flow - Head to Velocity Calculator
This calculator can be used to calculate air velocity in a duct or air stream from a measured head of water column. The dynamic pressure as head is typically measured with a pitot tube .
Charts are based on air density 1.205 kg/m3 and water density 1000 kg/m3 .
Air Flow - Velocity Heads
Table based on ρf = 1.205 kg/m3 (C = 4005, temperature 70 oF) and ρw = 1000 kg/m3 (1.940 slugs/ft3 ) .
Velocity Heads vs. Air Flow Velocities
Air Flow Velocity
- v -
(ft/sec)
Velocity Head
- hw -
(ft H2O)
5 0.00047
10 0.0019
15 0.0042
20 0.0075
25 0.012
30 0.017
35 0.023
40 0.030
45 0.038
50 0.047
55 0.057
60 0.067
65 0.079
70 0.092
75 0.11
80 0.12
85 0.14
90 0.15
95 0.17
100 0.19
  • The Engineering ToolBox (2005). Velocity Pressure Head. [online] Available at: https://www.engineeringtoolbox.com/velocity-head-d_916.html [Accessed Day Month Year].