The power factor of an AC electric power system is defined as the ratio active (true or real) power to apparent power , where

  • Active (Real or True) Power is measured in watts ( W ) and is the power drawn by the electrical resistance of a system doing useful work
  • Apparent Power is measured in volt-amperes (VA) and is the voltage on an AC system multiplied by all the current that flows in it. It is the vector sum of the active and the reactive power
  • Reactive Power is measured in volt-amperes reactive ( VAR ). Reactive Power is power stored in and discharged by inductive motors, transformers and solenoids

Reactive power is required for the magnetization of an electric motor but does not perform any work. Reactive power required by inductive loads increases the amounts of apparent power -  and the required supply to the grid from the power supplier to the distribution system.

Increased reactive and apparent power will decrease the power factor - PF .

Power Factor

It is common to define the Power Factor - PF - as the cosine of the phase angle between voltage and current - or the " cosφ ":

PF = cos φ

where

PF = power factor

φ = phase angle between voltage and current

power factor active true reactive apparent power

The power factor defined by IEEE and IEC is the ratio between the applied active (true) power - and the apparent power , and can in general be expressed as:

PF = P / S (1)

where

PF = power factor

P = active (true or real) power (Watts)

S = apparent power (VA, volts amps)

A low power factor is the result of inductive loads such as transformers and electric motors. Unlike resistance loads creating heat by consuming kilowatts, inductive loads require a current flow to create magnetic fields to produce the desired work.

Power factor is an important measurement in electrical AC systems because

  • an overall power factor less than 1 indicates that the electricity supplier need to provide more generating capacity than actually required
  • the current waveform distortion that contributes to reduced power factor is caused by voltage waveform distortion and overheating in the neutral cables of three-phase systems

International standards such as IEC 61000-3-2 have been established to control current waveform distortion by introducing limits for the amplitude of current harmonics.

Example - Power Factor

A industrial plant draws 200 A at 400 V and the supply transformer and backup UPS is rated 400 V x 200 A = 80 kVA .

If the power factor - PF - of the loads is 0.7 - only

80 kVA × 0.7

= 56 kW

of real power is consumed by the system. If the power factor is close to 1 (a purely resistive circuit) the supply system with transformers, cables, switch-gear and UPS could be made considerably smaller.

  • Any power factor less than 1 means that the circuit's wiring has to carry more current than what would be necessary with zero reactance in the circuit to deliver the same amount of (true) power to the resistive load.

Conductor Cross-Section vs. Power Factor

Required cross-section area of conductor with lower power factor:

Conductor Cross-Section vs. Power Factor
Power Factor 1 0.9 0.8 0.7 0.6 0.5 0.4 0.3
Cross-Section 1 1.2 1.6 2.04 2.8 4.0 6.3 11.1

A low power factor is expensive and inefficient and some utility companies may charge additional fees when the power factor is less than 0.95 . A low power factor will reduce the electrical system's distribution capacity by increasing the current flow and causing voltage drops.

"Leading" or "Lagging" Power Factors

A Power Factor is usually stated as "leading" or "lagging" to show the sign of the phase angle.

  • With a purely resistive load the current and voltage changes polarity in step and the power factor will be 1 . Electrical energy flows in a single direction across the network in each cycle.
  • Inductive loads - transformers, motors and wound coils - consumes reactive power with current waveform lagging the voltage.
  • Capacitive loads - capacitor banks or buried cables - generates reactive power with current phase leading the voltage.

Inductive and capacitive loads stores energy in magnetic or electric fields in the devices during parts of the AC cycles. The energy is returned back to the power source during the rest of the cycles.

In systems with mainly inductive loads - typically industrial plants with many electric motors - the lagging voltage are compensated with capacitor banks.

Power Factor for a Three-Phase Motor

The total power required by an inductive device like a motor or similar consists of

  • Active (true or real)  power (measured in kilowatts, kW)
  • Reactive power - the nonworking power caused by the magnetizing current, required to operate the device (measured in kilovars, kVAR)

The power factor for a three-phase electric motor can be expressed as:

PF = P / [(3) 1/2 U I] (2)

where

PF = power factor

P = power applied (W, watts)

U = voltage (V)

I = current (A, amps)

- or alternatively:

P = (3) 1/2 U I PF

= (3) 1/2 U I cos φ (2b)

U, l and cos φ are normally quoted on the motor nameplate.

Typical Motor Power Factors

Electrical Motors - Typical Power Factors
Power
(hp)
Speed
(rpm)
Power Factor (cos φ )
Unloaded1/4 load1/2 load3/4 loadfull load
0 - 5 1800 0.15 - 0.20 0.5 - 0.6 0.72 0.82 0.84
5 - 20 1800 0.15 - 0.20 0.5 - 0.6 0.74 0.84 0.86
20 - 100 1800 0.15 - 0.20 0.5 - 0.6 0.79 0.86 0.89
100 - 300 1800 0.15 - 0.20 0.5 - 0.6 0.81 0.88 0.91
  • 1 hp = 745.7 W

Power Factor by Industry

Typical un-improved power factors:

Electrical Motors - Power Factors by Industry
IndustryPower Factor
Brewery 75 - 80
Cement 75 - 80
Chemical 65 - 75
Electro-chemical 65 - 75
Foundry 75 - 80
Forging 70 - 80
Hospital 75 - 80
Manufacturing, machines 60 - 65
Manufacturing, paint 65 - 70
Metalworking 65 - 70
Mine, coal 65 - 80
Office 80 - 90
Oil pumping 40 - 60
Plastic production 75 - 80
Stamping 60 - 70
Steel works 65 - 80
Textiles 35 - 60

Benefits of Power Factor Corrections

  • reduced power bills - avoiding low power factor penalty from the utility power company
  • increased system capacity - additional loads can be added without overloading the system
  • improved system operating characteristics by reduced line loss - due to less current
  • improved system operating characteristics by gaining voltage - excessive voltage drops are avoided

Power Factor Correction with Capacitor

Electrical Motors - Power Factor Correction with Capacitor

Power factor before improvement (cosΦ)
Capacitor correction factor
Power factor after improvement (cosΦ)
1.00.990.980.970.960.950.940.930.920.910.90
0.50 1.73 1.59 1.53 1.48 1.44 1.40 1.37 1.34 1.30 1.28 1.25
0.55 1.52 1.38 1.32 1.28 1.23 1.19 1.16 1.12 1.09 1.06 1.04
0.60 1.33 1.19 1.13 1.08 1.04 1.01 0.97 0.94 0.91 0.88 0.85
0.65 1.17 1.03 0.97 0.92 0.88 0.84 0.81 0.77 0.74 0.71 0.69
0.70 1.02 0.88 0.81 0.77 0.73 0.69 0.66 0.62 0.59 0.56 0.54
0.75 0.88 0.74 0.67 0.63 0.58 0.55 0.52 0.49 0.45 0.43 0.40
0.80 0.75 0.61 0.54 0.50 0.46 0.42 0.39 0.35 0.32 0.29 0.27
0.85 0.62 0.48 0.42 0.37 0.33 0.29 0.26 0.22 0.19 0.16 0.14
0.90 0.48 0.34 0.28 0.23 0.19 0.16 0.12 0.09 0.06 0.02
0.91 0.45 0.31 0.25 0.21 0.16 0.13 0.09 0.06 0.02
0.92 0.43 0.28 0.22 0.18 0.13 0.10 0.06 0.03
0.93 0.40 0.25 0.19 0.15 0.10 0.07 0.03
0.94 0.36 0.22 0.16 0.11 0.07 0.04
0.95 0.33 0.18 0.12 0.08 0.04
0.96 0.29 0.15 0.09 0.04
0.97 0.25 0.11 0.05
0.98 0.20 0.06
0.99 0.14

Power factor correction with capacitors

Example - Improving power factor with capacitor

An electrical motor with power 150 kW has power factor before improvement cosΦ = 0.75 .

For a required power factor after improvement cosΦ = 0.96 - the capacitor correction factor is 0.58 .

The required KVAR capacity can be calculated as

C = (150 kW) 0.58

= 87 KVAR

Suggested Capacitor Ratings for T-Frame NEMA Class B Motors

Recommended sizes of KVAR units needed for correction of induction motors to approximately 95% power factor.

Induction Motors - KVAR Correction Units
Induction Motor Rating
(HP)
Nominal Motor Speed (rpm)
360018001200
Capacitor Rating
(KVAR)
Reduction of Line Current
(%)
Capacitor Rating
(KVAR)
Reduction of Line Current
(%)
Capacitor Rating
(KVAR)
Reduction of Line Current
(%)
3 1.5 14 1.5 23 2.5 28
5 2 14 2.5 22 3 26
7.5 2.5 14 3 20 4 21
10 4 14 4 18 5 21
15 5 12 5 18 6 20
20 6 12 6 17 7.5 19
25 7.5 12 7.5 17 8 19
30 8 11 8 16 10 19
40 12 12 13 15 16 19
50 15 12 18 15 20 19
60 18 12 21 14 22.5 17
75 20 12 23 14 25 15
100 22.5 11 30 14 30 12
125 25 10 36 12 35 12
150 30 10 42 12 40 12
200 35 10 50 11 50 10
250 40 11 60 10 62.5 10
300 45 11 68 10 75 12
350 50 12 75 8 90 12
400 75 10 80 8 100 12
450 80 8 90 8 120 10
500 100 8 120 9 150 12

Related Topics

  • Electrical

    Electrical engineering with units, amps and electrical wiring. Wire gauges, electrical formulas, motors and more.

Related Documents

Search

Search is the most efficient way to navigate the Engineering ToolBox.

Engineering ToolBox - SketchUp Extension - Online 3D modeling!

3D Engineering ToolBox Extension to SketchUp - add parametric components to your SketchUp model

Add standard and customized parametric components - like flange beams, lumbers, piping, stairs and more - to your Sketchup model with the Engineering ToolBox - SketchUp Extension - enabled for use with older versions of the amazing SketchUp Make and the newer "up to date" SketchUp Pro . Add the Engineering ToolBox extension to your SketchUp Make/Pro from the Extension Warehouse !

Translate this Page

Translate this page to Your Own Language .

About the Engineering ToolBox!

Privacy Policy

We don't collect information from our users. More about

We use a third-party to provide monetization technologies for our site. You can review their privacy and cookie policy here.

You can change your privacy settings by clicking the following button: .

Citation

This page can be cited as

  • The Engineering ToolBox (2004). Three-Phase Electrtical Motors - Power Factor vs. Inductive Load. [online] Available at: https://www.engineeringtoolbox.com/power-factor-electrical-motor-d_654.html [Accessed Day Month Year].

Modify the access date according your visit.

3D Engineering ToolBox - draw and model technical applications! 2D Engineering ToolBox - create and share online diagram drawing templates! Engineering ToolBox Apps - mobile online and offline engineering applications!

Unit Converter

















































5.8.12

.